    Re: Pressure drop through the suction line accumulator?



    Interesting drawing, looks like a oil recovery bottle on a flooded ammonia evaporator.
    If not ammonia, could be anyones guess.
    I can see why you have a 2 bar delta P from evap to compressor, with 3/8 dry suction.



  2. #52
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Pressure drop through the suction line accumulator?

    OK, I went back and read the original ost again, its R134A. Could still be a scavenge oil recovery line that rises up in vessel to control level, the 1/4 "line would restrict flow and limit it. Also the 3/8 dry suction may be intentional to restrict carry over.
    What controls liquid feed to flooded evaporator ?

  3. #53
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by lowcool View Post
    frank if suction line diameter is fixed by size of accumulator port,what the hell happened.when anyone has a vague out i call it the autoduhh syndrome it can happen any time.
    the inlet of accumulator is fixed, but you can use adaptor to reduce the diamter

  4. #54
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by desA View Post
    I think your compressor is going to suffer the world of pain, sooner, rather than later...
    why do you think so? sooner not later?

  5. #55
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Gary View Post
    That's a flooded evaporator... and a whole different ball game.
    as i said before, this system is taken over from other people. so i want to figure out the problem.
    do u have any suggestion on this so-called flooded evaporator?
    thanks a lot

  6. #56
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Magoo View Post
    OK, I went back and read the original ost again, its R134A. Could still be a scavenge oil recovery line that rises up in vessel to control level, the 1/4 "line would restrict flow and limit it. Also the 3/8 dry suction may be intentional to restrict carry over.
    What controls liquid feed to flooded evaporator ?
    what do u mean by "scavenge oil recovery line that rises up in vessel to control level"?
    can u elaborate it?
    before the evaporator, there is a manual valve to control the feeding liquid.

  7. #57
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by frank721 View Post
    why do you think so? sooner not later?
    My concern is about liquid slugs getting into the compressor, if the system is not controlled carefully.

    If that's all taken care of & guaranteed as a non-event, then rest easy - if not, then you may want to research further.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  8. #58
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Pressure drop through the suction line accumulator?

    dunno here we go years ago came across this sort of cascade system and i reckon that something like this was used on the expansion recovery,over run what ever circuit,come suction accumulator what ever to keep the feed up to the refrigerant pump.must say it was a little bit bigger on sizing but.ammonia blokes should have an idea
    anybody else good for ideas
    mmm to beer or not to beer...........lets drink breakfast

  9. #59
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Pressure drop through the suction line accumulator?

    The 1/4 inch pipe you mentioned is usually a support pipe . I have in one instance noticed that one of the pipe tilts if you test the accumulator indepedently . So to my knowledge it is a support pipe . Just check with manufacturer . Besides, give me the following data to select the right model for you to compare.
    Refrigerant
    evap capacity
    condensing temp
    evaporation temp .

  10. #60
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by desA View Post
    My concern is about liquid slugs getting into the compressor, if the system is not controlled carefully.

    If that's all taken care of & guaranteed as a non-event, then rest easy - if not, then you may want to research further.
    ok, then what do u think shoud be taken care?

  11. #61
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by lowcool View Post
    dunno here we go years ago came across this sort of cascade system and i reckon that something like this was used on the expansion recovery,over run what ever circuit,come suction accumulator what ever to keep the feed up to the refrigerant pump.must say it was a little bit bigger on sizing but.ammonia blokes should have an idea
    anybody else good for ideas
    thanks, any experience on R134a?

  12. #62
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by D.D.KORANNE View Post
    The 1/4 inch pipe you mentioned is usually a support pipe . I have in one instance noticed that one of the pipe tilts if you test the accumulator indepedently . So to my knowledge it is a support pipe . Just check with manufacturer . Besides, give me the following data to select the right model for you to compare.
    Refrigerant
    evap capacity
    condensing temp
    evaporation temp .
    Refrigerant : R134a
    evap capacity:1~1.5kW
    condensing temp:40~50 degree C
    evaporation temp:15 degree C

    Thanks a lot! by the way how to transfer cooling capacity in unit of "tons of R22" to "kW of R134a"?

Page 2 of 2 FirstFirst 12

Similar Threads

  1. what is useful of Economizer?
    By Ahmed.ragab in forum Industrial Compressors
    Replies: 33
    Last Post: 18-08-2010, 12:15 PM
  2. high liquid line pressure?
    By TECH TIM in forum Commercial
    Replies: 5
    Last Post: 09-05-2009, 05:36 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. Hot Gas defrost suction pressure regulation
    By 87mustang in forum Technical Speculations
    Replies: 5
    Last Post: 05-08-2005, 07:25 AM
  5. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Replies: 32
    Last Post: 08-05-2002, 05:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •