    Smile Pressure drop through the suction line accumulator?



    Now I am using a suction line accumulator (R134a) between my evaporator and compressor. I measured that the pressure of evaporator is about 3 bar but the inlet pressure of compressor is about 1bar. That means accumulator caused the pressure drop of 2 bar.

    My dear friends, is it normal that accumulator results in such big pressure drop? I am not quite clear about the inner structure of accumulator. Is there any bolck or mesh in the accumulator which could induce the pressure drop?

    Thanks a lot!



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pressure drop through the suction line accumulator?

    Pressure drop of suction accumulator is about 0.3°C.

    What is make and model # of your accumulator?

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Pressure drop through the suction line accumulator?

    Full of liquid.
    Debris is almost not possible, most don't have mesh filters in it.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Smile Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by nike123 View Post
    Pressure drop of suction accumulator is about 0.3°C.

    What is make and model # of your accumulator?
    You mean the pressure drop is 0.3bar nomally, right?
    I am using Emerson A-AS-597

    Thanks a lot.

  5. #5
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Smile Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Peter_1 View Post
    Full of liquid.
    Debris is almost not possible, most don't have mesh filters in it.
    What do mean by "full of liquid"?

    I found there is a so-called oil return orifice at the bottom of the U tube. But I can't see the exact posion and structure clealy there. Would you please elaborate it?

    Thanks a lot.

  6. #6
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Pressure drop through the suction line accumulator?

    design kw rating of evap & comp at what suction temp would be good to see.sounds to me your suction line is undersized,only accumulator prob ive had is the tube falling off inside.
    mmm to beer or not to beer...........lets drink breakfast

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by frank721 View Post
    You mean the pressure drop is 0.3bar nomally, right?
    I am using Emerson A-AS-597

    Thanks a lot.
    No, I mean equivalent pressure drop of 0,3°C!

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by frank721 View Post
    I found there is a so-called oil return orifice at the bottom of the U tube. But I can't see the exact posion and structure clealy there. Would you please elaborate it?

    Thanks a lot.



    I don't think that "full of liquid" state could make pressure drop in range of 2 bar.

  9. #9
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Pressure drop through the suction line accumulator?

    R-134a @ 0.3'C dP

    = (0.3/1.1)*13.3 kPa
    = 3.63kPa
    = 0.0363 bar

    Source 'Application Guide AG 31-011' "Refrigerant piping design guide", McQuay
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Pressure drop through the suction line accumulator?

    I don't think that "full of liquid" state could make pressure drop in range of 2 bar.[/QUOTE]
    In another thread on this forum, you will find this actual situation which isn't resolved yet. Even a bigger pressure drop Nike of 2 bar
    Last edited by Peter_1; 22-06-2009 at 08:04 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Peter_1 View Post
    In another thread on this forum, you will find this actual situation which isn't resolved yet. Even a bigger pressure drop Nike of 2 bar
    Could the inlet & outlet be connected incorrectly?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Pressure drop through the suction line accumulator?

    I suspect there is something else between the evap and the compressor. Perhaps a suction drier or an EPR valve... or maybe a kink in the line.

    Check the suction line temperature from the evap to the compressor. Where you find a temperature drop you will find the pressure drop.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Peter_1 View Post
    In another thread on this forum, you will find this actual situation which isn't resolved yet. Even a bigger pressure drop Nike of 2 bar
    Could be, but I still don't see how liquid could make any effect to that pressure drop if accumulator is in perfect condition.

  14. #14
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Smile Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by lowcool View Post
    design kw rating of evap & comp at what suction temp would be good to see.sounds to me your suction line is undersized,only accumulator prob ive had is the tube falling off inside.
    the diameter of the suctionline is fixed by the port of the accumulator.

    What do you mean by "only accumulator prob ive had is the tube falling off inside"?

    Thanks

  15. #15
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Pressure drop through the suction line accumulator?

    .


    Many heat pumps of Far Eastern or Japanese manufacture incorporate a wire mesh filter in the inlet pipe at the top of the accumulator.

    These are mostly unmarked, little more than the diameter of the pipe and often block with debris.

    You need to cut the whole thing out to locate it.

    I have also seen them be fitted the wrong way around (i.e. reversed flow) at the factory.


    .

  16. #16
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Pressure drop through the suction line accumulator?

    Hello Frank.
    ? Are you speaking about that L'Unite Hermetique from your thread: http://www.refrigeration-engineer.co...ad.php?t=18967
    If yes, could you please give other parameters, such as room temp, evap dT, SH, presupposing 3 Bar is evap pressure.

  17. #17
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Pressure drop through the suction line accumulator?

    gday frank nikes photo depicts the said tube internally,you can hang any size suction line off the fitting ie lets say long pipe run requires larger size piping,size of accumulator ports is only relevant to capacity (kw) of system.5/8" accumulator with 1 1/8" pipe run
    mmm to beer or not to beer...........lets drink breakfast

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Peter_1 View Post
    In another thread on this forum, you will find this actual situation which isn't resolved yet. Even a bigger pressure drop Nike of 2 bar
    You mean this one?

    Pressure drop there is 1,9 Bar.

  19. #19
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Pressure drop through the suction line accumulator?

    Ciao,

    Interesting debate, it appears to be a large pressure drop to be caused by an accumulator full of liquid, what is the pipe temperature at the accumulator inlet/outlet and the compressor inlet?

    Cheers
    Tutto il Mondo e un Paese

  20. #20
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pressure drop through the suction line accumulator?

    frank721

    As Gary already pointed out, when there is pressure drop, there is temperature drop.
    Measure accumulator inlet pipe and outlet pipe temperature ((and post your findings here).
    If difference is greater than 0,5°C you have restriction in accumulator. If not, your problem is elsewhere.

  21. #21
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by nike123 View Post
    As Gary already pointed out, when there is pressure drop, there is temperature drop.
    Not in the gaseous phase
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  22. #22
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Peter_1 View Post
    Not in the gaseous phase
    Why is then, when I making pressure test with nitrogen, nitrogen bottle is cooled?

  23. #23
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Peter_1 View Post
    Not in the gaseous phase
    That's true... but with this much restriction I'm thinking we can assume a liquid/vapor mixture before the restriction... especially if it has a liquid filled accumulator.

    But then, we don't have enough information about the system.

    Is this a cooler or a freezer?

    Is it a cap tube system or a TXV system?

  24. #24
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by nike123 View Post
    Why is then, when I making pressure test with nitrogen, nitrogen bottle is cooled?
    Because the bottle has both liquid and vapor.

  25. #25
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Gary View Post
    Because the bottle has both liquid and vapor.
    I taught that nitrogen in bottle is at max 200bar and that all nitrogen is boiled at that pressure (and in gaseous phase) when at ambient temperature.


  26. #26
    Join Date
    Jan 2007
    Location
    scotland
    Age
    46
    Posts
    159
    Rep Power
    18

    Re: Pressure drop through the suction line accumulator?

    why not fit shreader tails into inlet/outlet sides of accumulator,if anything it will tell you if it is the problem.dont like them myself as they ushally just become large oil traps on our old hot gas systems.

  27. #27
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Gary View Post
    That's true... but with this much restriction I'm thinking we can assume a liquid/vapor mixture before the restriction... especially if it has a liquid filled accumulator.

    But then, we don't have enough information about the system.

    Is this a cooler or a freezer?

    Is it a cap tube system or a TXV system?
    That's also what I'm thinking about it.
    Give us some more information.

    What's your SH on the evaporator? What's the pressure inside your accumulator and what's its shell temperature? That's how we found out it was full of liquid.
    Install schraeders as Fowlie suggested and share this readings
    Nike, at least no noticeable temperature drop, perhaps you can see it with an IR imaged scanner, perhaps..
    A pressure reduction of a gas can be perfectly isothermic
    Last edited by Peter_1; 23-06-2009 at 07:15 AM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  28. #28
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Pressure drop through the suction line accumulator?

    My believe is any gas pressed, then cooled down to ambient, during sudden expanding will always consume SOME heat (insufficient however at all for refrigeration). And using nitrogen, we deal with a huge expansion - from 200Bg down to 20-30Bg (then to 0 Bg). But not so huge gas transition is here - only from 3B to 1B.
    Frank meanwhile, is not giving the whole picture, having drawn onto the scene only that partricular part of his system.

  29. #29
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Pressure drop through the suction line accumulator?

    is the accumulator to small?a reply from the original poster would be good
    mmm to beer or not to beer...........lets drink breakfast

  30. #30
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    dear freinds. sorry for late reply, since i was on leave in this period. it was not convenient for me to use internet.
    now, let's continue. i feel so warm here because you are so kind.

  31. #31
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by nike123 View Post



    I don't think that "full of liquid" state could make pressure drop in range of 2 bar.
    Hi, can you show me some more pictures or schematics with more detail? I am curious about it. Thanks a lot

  32. #32
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Talking Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Gary View Post
    I suspect there is something else between the evap and the compressor. Perhaps a suction drier or an EPR valve... or maybe a kink in the line.

    Check the suction line temperature from the evap to the compressor. Where you find a temperature drop you will find the pressure drop.
    Thanks for your suggestion. there is no other device between the accumulator and compressor. But you bring a good point: kink in the line. In fact, the diameter of outlet of accumulator is 7/8" and diameter of inlet of compressor is 5/8", but they are connected with a smaller tube of 1/4"
    is it the reason that cause the big pressure drop?

  33. #33
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Argus View Post
    .


    Many heat pumps of Far Eastern or Japanese manufacture incorporate a wire mesh filter in the inlet pipe at the top of the accumulator.

    These are mostly unmarked, little more than the diameter of the pipe and often block with debris.

    You need to cut the whole thing out to locate it.

    I have also seen them be fitted the wrong way around (i.e. reversed flow) at the factory.


    .
    wow... it's hard for me to cut it. anyway, it's a possible reason. thanks

  34. #34
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Yuri B. View Post
    Hello Frank.
    ? Are you speaking about that L'Unite Hermetique from your thread: http://www.refrigeration-engineer.co...ad.php?t=18967
    If yes, could you please give other parameters, such as room temp, evap dT, SH, presupposing 3 Bar is evap pressure.
    Hi, that thread is also posted by me. room temp is 31 degree C, SH is about 5 degree C
    sorry, what do u mean by evap dT?

  35. #35
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Gary View Post
    That's true... but with this much restriction I'm thinking we can assume a liquid/vapor mixture before the restriction... especially if it has a liquid filled accumulator.

    But then, we don't have enough information about the system.

    Is this a cooler or a freezer?

    Is it a cap tube system or a TXV system?
    it's cooler and TXV system

  36. #36
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by lowcool View Post
    is the accumulator to small?a reply from the original poster would be good
    i think it's already oversize according to my cooling capacity.

  37. #37
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Pressure drop through the suction line accumulator?

    Hi Frank.
    What temp air off evap ?

  38. #38
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Pressure drop through the suction line accumulator?

    And what the RH of the 31C air by the way?

  39. #39
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by frank721 View Post
    Thanks for your suggestion. there is no other device between the accumulator and compressor.
    Are there any devices between the evaporator and the accumulator?

  40. #40
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by frank721 View Post
    it's cooler and TXV system
    After reading your other thread, I am even more confused. This is either an A/C system or it is a cooler system that you are trying to convert to an A/C system. Which is it?

  41. #41
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by frank721 View Post
    Thanks for your suggestion. there is no other device between the accumulator and compressor. But you bring a good point: kink in the line. In fact, the diameter of outlet of accumulator is 7/8" and diameter of inlet of compressor is 5/8", but they are connected with a smaller tube of 1/4"
    is it the reason that cause the big pressure drop?
    Are you serious? A 1/4" connecting line?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  42. #42
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by desA View Post
    Are you serious? A 1/4" connecting line?
    I read that several times and it just didn't register that anyone would actually do that... lol

  43. #43
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by frank721 View Post
    In fact, the diameter of outlet of accumulator is 7/8" and diameter of inlet of compressor is 5/8", but they are connected with a smaller tube of 1/4"
    is it the reason that cause the big pressure drop?
    Yes... that would definitely do it.

  44. #44
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Yuri B. View Post
    Hi Frank.
    What temp air off evap ?
    hi, my evaporator is used for liquid cooling like cooling system in the desktop now. so, there is no air off evap

  45. #45
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    Quote Originally Posted by Gary View Post
    Are there any devices between the evaporator and the accumulator?
    Quote Originally Posted by Gary View Post
    After reading your other thread, I am even more confused. This is either an A/C system or it is a cooler system that you are trying to convert to an A/C system. Which is it?
    Quote Originally Posted by desA View Post
    Are you serious? A 1/4" connecting line?
    Quote Originally Posted by Gary View Post
    I read that several times and it just didn't register that anyone would actually do that... lol
    yes, it is 1/4" really.
    there is a needle valve between the evap and accumulator. but it is fully open. pressure drop is not significant when fully open.
    it seems that we have found the cause of the 2 bar pressure drop:7/8" to 1/4"
    thanks a lot, my friends

  46. #46
    Join Date
    Feb 2009
    Location
    Sigapore
    Posts
    47
    Rep Power
    0

    Re: Pressure drop through the suction line accumulator?

    For discussing conveniently, i post the schematic of the evaporator. i measured the pressures at Point 1 and 2.
    Attached Images Attached Images

  47. #47
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Pressure drop through the suction line accumulator?

    frank if suction line diameter is fixed by size of accumulator port,what the hell happened.when anyone has a vague out i call it the autoduhh syndrome it can happen any time.
    mmm to beer or not to beer...........lets drink breakfast

  48. #48
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Pressure drop through the suction line accumulator?

    interesting picture whats it of frank
    mmm to beer or not to beer...........lets drink breakfast

  49. #49
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Pressure drop through the suction line accumulator?

    I think your compressor is going to suffer the world of pain, sooner, rather than later...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  50. #50
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Pressure drop through the suction line accumulator?

    That's a flooded evaporator... and a whole different ball game.

Page 1 of 2 12 LastLast

Similar Threads

  1. what is useful of Economizer?
    By Ahmed.ragab in forum Industrial Compressors
    Replies: 33
    Last Post: 18-08-2010, 12:15 PM
  2. high liquid line pressure?
    By TECH TIM in forum Commercial
    Replies: 5
    Last Post: 09-05-2009, 05:36 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. Hot Gas defrost suction pressure regulation
    By 87mustang in forum Technical Speculations
    Replies: 5
    Last Post: 05-08-2005, 07:25 AM
  5. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Replies: 32
    Last Post: 08-05-2002, 05:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •