    Question Manual Vi setting for Howden WRVi255



    We are going to replace a Howden MK5/WCV255 with Howden MK6/WRVi. New compressor is supplied by a package supplier saying that the WRVi is direct replacement of WCV. WRVi model consists of a manual Vi setting in the range of 2.2 to 5.0 turning a square headed knob located below shaft on drive side end cover. For 2.2 Vi, the knob has to be rotated clockwise and for 5.0 Vi, it has to be rotated anticlockwise. WCV model don't have such a knob.

    My question is what should be the initial setting of Vi when making the test run? What will be final and permanent setting for continuous operation. I am new to this field and don't have much experience for Howden.



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Manual Vi setting for Howden WRVi255

    I know this should be in SI units, but I have to run off and just have a couple of minutes.
    VI=Discharge Pressure (absolute) divided by absolute Suction Pressure. An example is 5lbs suction and 150lbs discharge. Add 14.7lbs to the suction for absolute suction pressure (19.7lbs) Add 14.7 to the discharge (164.7). Divide 164.4 by 19.7=8.3 ideal VI.
    You will note that unless your head is quite low or your suction quite high, you may always be under compressing.
    Most adjustable VI Compressors are used in two stage systems or medium or high temp applications.
    Most screws top out about around 5.0 VI.

  3. #3
    Join Date
    Jun 2009
    Location
    UK
    Posts
    7
    Rep Power
    0

    Re: Manual Vi setting for Howden WRVi255

    Please share Howden WRV204-11058 standard CI Oil injected screw compressor service manual

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Manual Vi setting for Howden WRVi255

    If you can give us your suction discharge pressures will pass on corect Vi setting .
    I would have thought package supplier should give you the info and manual as part of the deal .

  5. #5
    Join Date
    Mar 2009
    Location
    Saudi Arabia
    Posts
    18
    Rep Power
    0

    Re: Manual Vi setting for Howden WRVi255

    Yes, I got the confirmation from package supplier and OEM of compressor to set it to 5.0

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Manual Vi setting for Howden WRVi255

    Hi, desaipt2003

    please check attachment...

    .... resolution is not the best, due to upload limit of 100kb, but ..

    Best regards, Josip
    Attached Images Attached Images

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Mar 2009
    Location
    Saudi Arabia
    Posts
    18
    Rep Power
    0

    Re: Manual Vi setting for Howden WRVi255

    Dear all,

    We have replaced the compressor and did the pressure test, vacuuming, new refrigerant and oil charging. During the test run we are getting the trouble of high oil temperature. System is tripping on "Oil manifold High-High temperature" after 40-45 minutes of operation. Compressor discharge temperature reaches 115-120 deg. C against 95 deg. C in same system operating in our second plant. What can be the reason of high oil temperature?

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Manual Vi setting for Howden WRVi255

    Because your discharge temperatures are higher.
    The oil Temperature is higher!
    Is the 2 comps on a common discharge line.
    Or if they are separate then there is an issue at the condenser.
    Can't advise any further as I don't know your system.
    Please advise further.
    Grizzly

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Manual Vi setting for Howden WRVi255

    There are several things to point out on the limited info you have posted .

    Machine should not be even running with dicharge temp that high .
    Maximum is 100 deg C

    With WRC compressor it had no oil injection into rotors and it apparently ran ok .
    This would indicate a higher than normal oil tempreture affecting discharge temp .

    You need to supply the following .
    1 .refrigerant or gas being pumped
    2 .suction gas inlet temp to compressor
    3 .oil pressure above discharge pressure
    4 . description of oil circuit and process you are doing
    5 . Pressures you are operating at ie suction and discharge pressures .

  10. #10
    Join Date
    Mar 2009
    Location
    Saudi Arabia
    Posts
    18
    Rep Power
    0

    Re: Manual Vi setting for Howden WRVi255

    Dear Ranger1,

    1 .refrigerant or gas being pumped - R134a
    2 .suction gas inlet temp to compressor - varying
    3 .oil pressure above discharge pressure - 2to 3 kg/cm2
    4 . description of oil circuit and process you are doing-
    5 . Pressures you are operating at ie suction and discharge pressures - Suction : varying from 2.5 kg/cm2 at initial start up to 0.15 kg/cm2 at tripping time./ Discharge : 8 to 8.5 kg/cm2.

    The compressor is loading up upto 40% during first 5 minutes of operation and getting down agian to minimum (12-13%) within 3 minutes of capacity. \system trips on oil manifold temperature high-high.

    When consulted the vendor, they are telling that the system is short of refrigerant and it has to be charged with additional refrigerant in few steps and to watch the performance after each addition. Is shortage of refrigerant can be the potential reason from oil temperature hike?

  11. #11
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Manual Vi setting for Howden WRVi255

    What is complete serial number of machine ? We require rotor lenth .

    Also what type of oil cooler and how is it cooled ?

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Manual Vi setting for Howden WRVi255

    You have to regulate the slide injection oil port to control discharge temp.

  13. #13
    Join Date
    Mar 2009
    Location
    Saudi Arabia
    Posts
    18
    Rep Power
    0

    Re: Manual Vi setting for Howden WRVi255

    Dear Ranger1,

    Serial No. of machine is MK6B/WRVi255130/667.

    Oil cooler is shell and tube type heat exchanger with oil on shell side and cooling water on tube side. Oil flow through coller is controlled by a TCV(Temperature control valve). But I think that is not the matter of concern. We are getting high discharge temperature at compressor. As per vendor, due to shortage of refrigerant, it is getting superheated in evaporator which is causing the trouble of high discharge temperature and in turn high oil temperature.

  14. #14
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Manual Vi setting for Howden WRVi255

    Do you have reason to think that you are short of refrigerant ?

    What is oil temp , as i think its still important that this is working satisfactorarily ?

    To me not knowing what you are cooling , it seems odd that compressor can load up and achieve set point and unload in very short time .
    Maybe things are short of refrigerant as only this and oil cooling could cause these tempretures .
    Is oil cooler running to its max capacity
    with control valve fuuly open ?
    It should probably be cleaned out anyway .

    I would have thought discharge temp should be below 60 deg C with 10 deg C s/heat and 80 deg C with 30 deg C s/heat .

    There is no oil injection to cool discharge gas so its more than likely s/heat due to low refrigerant charge and/or oil cooler not working as well .

Similar Threads

  1. Setting indoor fan speed Daikin VRV-S
    By mchild in forum Air Conditioning
    Replies: 4
    Last Post: 24-04-2009, 09:38 PM
  2. Creating Troubleshoot manaul (Fault Code Manual)
    By Roan in forum Trouble Shooting
    Replies: 2
    Last Post: 25-02-2009, 08:11 PM
  3. Replies: 6
    Last Post: 04-01-2009, 07:30 PM
  4. LP switch pressure setting for Pump Down of Chiller
    By venugopal in forum Technical Discussions
    Replies: 9
    Last Post: 12-11-2006, 07:18 PM
  5. HP Switches (Manual or Auto)
    By Latte in forum Technical Discussions
    Replies: 9
    Last Post: 02-06-2005, 07:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •