    Lennox unit head pressure control



    Last year i posted about a lennox unit we had inherited on a maintenance contract.
    KVHK48.DVFC

    http://www.refrigeration-engineer.co...ghlight=lennox

    Since that post we have had so many problems with it it's untrue.
    I got called to it the other day and circuit 2 was tripping on HP ( which is controlled by dampers ).
    I checked the dampers and they were closed when the pressure was 24 bar. The dampers aren't seized and the actuator does move.

    I can't find a service manual anywhere for this model and i tried to contact lennox but got no answer.

    Does anyone know the range the dampers are supposed to work between?

    Also what controlls it? I noticed a pressure transducer on circuit 1 but nothing on circuit 2.
    There is only 1 actuator that controlls the dampers for both circuit 1 and 2.


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Lennox unit head pressure control

    Hi Marc
    Logically they would be pressure controlled, obviously what refrigerant you are running on.
    Would have huge bearing upon what your head pressure control of the dampers would be!
    Like you I cannot find reference to this unit on the Lennox website.
    What do you think?
    Grizzly

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Lennox unit head pressure control

    I managed to find a manual but it isn't much help, the unit is on r407c.
    http://www.lennoxeurope.com/transfer..._KVHK-0404.pdf

    It doesn't say much about the Condensing pressure control only on page 20
    "Based on 2 dampers on the outdoor unit discharge air, which lets you control condensation temperature through air flow
    The damper is moving by a servomotor, which receives a proportional signal throughnanpressure detector".

    One thing that i noticed is that on page 9 it says minimum on coil temp of the indoor unit is +15C on cooling but the indoor is in the carpark outside and the air is ducted upstairs.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Lennox unit head pressure control

    Haven't found a manual yet but found some spec details if you want...

    http://pdf.directindustry.com/pdf/le...29175-_34.html

    Bottom of page 34/192

    edit:
    There you go, one Manual..

    http://www.lennoxeurope.com/transfer..._KVHK-0404.pdf
    Last edited by Brian_UK; 19-06-2009 at 10:23 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Lennox unit head pressure control

    Thanks for that Brian.
    The manual doesn't show anything about the head pressure control- what a surprise.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Lennox unit head pressure control

    Just says that it is a electric servo motor run off pressure transducers. As you have already said, sorry must read deeper into your posts. DOH!
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Alco/Emerson head master/condensor pressure control
    By liptow in forum Fundamentals
    Replies: 1
    Last Post: 13-05-2009, 01:50 PM
  2. Lennox Unit problem
    By marc5180 in forum Air Conditioning
    Replies: 9
    Last Post: 13-12-2007, 09:20 PM
  3. Control scenario
    By Mike Hopkins in forum Technical Discussions
    Replies: 5
    Last Post: 14-09-2007, 11:25 AM
  4. High head pressure no duty
    By LRAC in forum Commercial
    Replies: 15
    Last Post: 23-07-2007, 12:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •