    Mitsubishi FDC2501HKXRE2



    Hi,

    Need some advice please. Recently went to a vrv mitsi unit. had blown the inverter board.

    Mitsi no longer make the parts so we sent the board back to be fixed. Fitted it today and disconnected the comperessor to dry run. Bang goes the board.

    Mitsi arnt being very helpful in the matter and i am more used to and keyed up for daikin units.

    Mitsi say this is the only way of testing it, but as they no langer make the spare parts, looks like it mite be a rip out job.

    Has any one ever experienced this???

    Cheers, steve



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Mitsubishi FDC2501HKXRE2

    When did the board blow? Was it as soon as power was turned on or as soon as the compressor started up?

    Did you check the compressor was ok and not down to earth?

    I went to a system a few weeks back that kept blowing the board, i found that the other company that had replaced the compressor and inverter board had connected the compressor wrong on the inverter board.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    GREENCOLD's Avatar
    GREENCOLD Guest

    Re: Mitsubishi FDC2501HKXRE2

    Quote Originally Posted by marc5180 View Post
    When did the board blow? Was it as soon as power was turned on or as soon as the compressor started up?

    Did you check the compressor was ok and not down to earth?

    I went to a system a few weeks back that kept blowing the board, i found that the other company that had replaced the compressor and inverter board had connected the compressor wrong on the inverter board.
    Comp was disconected when i ran it. Blew when it went to start. Its not a normal inverter, caps and what not are all seperate from the main board. It seems like a very early one.

    Steve

  4. #4
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: Mitsubishi FDC2501HKXRE2

    This is an early model of inverter system so treat it gently.
    The inverter pcb is generally still available but the chips arn't so they need moving to the new board.
    I would suspect the problem is with the power transducer module which feeds the compressor and is controlled by the inverter.
    Brit

Similar Threads

  1. Few question about Mitsubishi Heavy Industrial air condition
    By fireduck in forum Air Conditioning
    Replies: 55
    Last Post: 12-05-2009, 02:35 PM
  2. [Ask] Mitsubishi rotary compressor
    By felixfab_93 in forum Refrigeration Books
    Replies: 1
    Last Post: 18-12-2008, 10:48 AM
  3. Mitsubishi inverter problem
    By R1976 in forum Air Conditioning
    Replies: 3
    Last Post: 16-06-2008, 09:54 PM
  4. Mitsubishi Light Truck Refrigeration
    By Mastercool in forum Transport
    Replies: 2
    Last Post: 23-11-2007, 06:15 AM
  5. Mitsubishi compressor lock
    By marc5180 in forum Air Conditioning
    Replies: 29
    Last Post: 08-10-2007, 05:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •