19-06-2009, 08:24 AM #1
Failing remote controller (daikin BRC1D527)
Our air conditioning system won't work.
The remote controller keeps showing the "external control" icon (the 3 little arrows pointing centerward) like some other control device would take over it.
Since such a device does not to exist we wonder what is the other signification of that icon.
If we tray any operation (setting timer, ...) it actually fails.
19-06-2009, 10:17 AM #2
Re: Failing remote controller (daikin BRC1D527)
the centralised control symbol as described above shows for a number of reasons
the first is there is some centralised controller connected, this could be a PC, a timer, a KRP time clock pcb or the like, if you are not sure try this. press test (bottom left) button on the RC for 6 seconds, the display will change, if it says 00 where the temperature is usually displayed YOU DO HAVE a centralised control device if it shows 10 you dont.
press test once to exit this mode.
the centralised control symbol also shows if the terminal T1 T2 are used they can be wired to any external switch i.e PIR or window switch. depending on the setting of the unit this can be used to shut the unit down and the centralised symbol will show again.
good luck hope this helps
graham (back working on the daikins)
20-06-2009, 06:04 PM #3
Thank you for your answer.
We found out where the problem comes from.
This is an apartment we just moved in (a colocation) and each of us was given a controller dedicated to setting the temperature in our respective rooms.
But it seems one controller was not given to us: the master controller which is the one used to set the general behaviour of the whole system.
Once we found this controller and switched it on, the remote controller on the wall stopped showing the icon I spoke about and we could set it up successfully.
22-06-2009, 01:56 PM #4
Just a quicky guys, one of our engineers diagnosed a PCB problem on a FAYP71LV1 high wall unit. Of course the enginner is on holiday, we replaced the indoor PCB but still no go. Power to PCB and a voltage out to control pad BRC1D52 i suspect the actual controller is faulty itself completly blank.
Any help much appreciated.Grumpy men live longer
22-06-2009, 08:51 PM #5
if you have 16 volts to the controller and there is no display it will be the controller itself then, a very rare instance.
Daikin controller
By mchild in forum Air ConditioningReplies: 8Last Post: 02-10-2009, 07:14 PM -
daikin remote
By slavex in forum Air ConditioningReplies: 0Last Post: 12-03-2009, 09:47 AM -
Daikin Controller
By mchild in forum Air ConditioningReplies: 11Last Post: 24-11-2008, 02:34 AM -
DAIKIN VRV Remote controller
By 2007eng in forum Air ConditioningReplies: 15Last Post: 19-07-2008, 07:04 PM -
daikin remote controller setting list
By knight rider in forum Air ConditioningReplies: 9Last Post: 21-05-2007, 10:10 PM