    Unhappy Grasso Head over heating need urgent help
    i am working on RC412 Grasso one of its head and cyclinder is over heating next to check valve , i have changed the check valve , also changed the head and vlve inside but it didnt worked and now changed the piston conecting rod and rings as well still it is over heating the seleve is clean . need urgent assistance and guide lines thanx
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Grasso Head over heating need urgent help
    Is the head where the safety valve is?
    Did you check against possible blow by of the safety valve?
    Pakistan
    9
    Quote Originally Posted by NoNickName View Post
    yes it is the head where safety valve is i have changed the safety valve as well any more suggestion on the safety vallve blow checking procedure will apreciate it
    495
    Hi salman is this a 2 stage compound compressor ,and is it the final discharge stage ,may be the other stages are not loading up fullly and the comression ratio is to high and causing high temperatures, or is the oring on top of the liner between the discharge plate missing and causing blow back of hot gas
    Pakistan
    9
    Quote Originally Posted by GHAZ View Post
    It is single stage compressor other pistons are working just fine
    Jul 2006
    865
    This may not be your problem, and probably is not, but it happened to me.
    I spent a Summer in a plant in Alaska. They had three RC-611 on a freezing tunnel.
    One of them had the paint burnt off one cylinder. I took it apart and did not see anything wrong. I pulled another head and found the safety head spring was an inch shorter that the other one.
    Mar 2006
    Merate (LC) - Italy
    2,549
    Ok, then, the problem is 99% due to the safety valve or high discharge pressure. The valve keeps blowing back hot gas to the suction. You can't test it when installed; you will have the remove it and test it on a rig.
    4,703
    Hi Salman.
    All the guys here are highly experienced and have given good advise.
    The general consensus is that there is something wrong within the individual cylinder and I tend to agree.
    read the following extracted from one of the GRASSO manuals.
    If there is any doubt about the proper performance
    of this LP pressure relief valve, then this relief valve
    should be renewed immediately. When a pressure
    relief valve works improperly, discharge gas starts
    circulating through the cylinder head, which makes
    this cylinder head feel much warmer compared to
    other cylinder heads.
    That having been said do not discount NH3LVR's comment.
    Sadly I think you will have to keep looking.
    Just a thought I know you have changed the LP relief valve.
    Did you check it's valve seat within it's housing for damage or foreign material stuck to it.
    What refrigerant are you running on?
    You could have a wire drawn seat?
    Good luck and don't forget to let us know how you got on!
    Sorry for asking the obvious but you could be having a bad day and forgot the obvious?
    I know I do sometimes!
    Apr 2009
    Durban
    70
    Hi Salman,
    Have you done a leak test on the discharge valve assembly on that cylinder ?
    May 2006
    India
    399
    what about superheat ? in nh3 excessive head heating could be traced to NMT 10K superheat .
    Pakistan
    9
    Quote Originally Posted by D.D.KORANNE View Post
    what is the best way for tracing super heat? NH3
    i am working on lp relief valve
    Pakistan
    9
    Thank you guys for all your help the problem has been sorted out it was gaskit in between the liner which had crumbled and was damaged because wasnt properly fitted correctly during the last maintenance.
    I am also buyer for RC12 series used compressors up to six cyclinder if you have any please contact me thanx again for all your help
    Apr 2009
    Durban
    70
    Hi Salman,
    Great to hear you came right, I'm a Grasso fan, good gear.
    Frank Day
  1. Grasso SP2 duo packs
    By aawood1 in forum NH3
    Last Post: 12-06-2009, 10:56 AM
  2. Modifying aricond. for heating, cooling and hot water
    By kimusabi in forum Technical Discussions
    Last Post: 10-10-2008, 07:28 AM
  3. Prestcold head bolt torque?
    By monkey spanners in forum Technical Discussions
    Last Post: 21-01-2008, 08:03 PM
  4. MV600 head pressure trip (ghost)
    By andre_fridge in forum Technical Discussions
    Last Post: 28-01-2006, 02:16 PM