    Unhappy Compressor run for 3 mins then off for 10 mins



    Hi there, please help me on the commercial refrigerator using r12 , compressor was run for 3 mins then off for 10 mins then on for 3 mins again and again but condenser fan and evolorator fan still runing , inside box is about 50F when the compressor run it's colder but only few mins , I was put my gauge on liquid line at drier reading 120F when compressor run and I was low side gauge at compressor process tube reading 10F when compressor run, ambient temp about 70F , You think this system is low charge, temp control or relay? Thank you for your help



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Compressor run for 3 mins then off for 10 mins

    based on the limited information, I would offer a guess that it's cycling on klixon due to overheating caused by a lack of refrigerant charge.

    A lot more information is need to make an educated diagnosis I'm afraid

  3. #3
    Join Date
    Apr 2009
    Location
    ireland
    Age
    53
    Posts
    12
    Rep Power
    0

    Re: Compressor run for 3 mins then off for 10 mins

    Hi there Sanya. The first thing Id check is Your condensor. Make sure its not gummed up especially if its in a kitchen. also some older units used an over pressure switch between comp and cond. They go faulty and depending how its wired will shut the whole unit down or just the comp.Hope its that simple.

  4. #4
    Join Date
    Apr 2009
    Location
    ireland
    Age
    53
    Posts
    12
    Rep Power
    0

    Re: Compressor run for 3 mins then off for 10 mins

    Also thought of klixon on comp. If thats dodgy it will shut down just the comp. Norm wont stay off that long unless the comp is running really hot.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor run for 3 mins then off for 10 mins

    My guess would be dirty condenser.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Compressor run for 3 mins then off for 10 mins

    And my guess is a low charge and low pressure control stops the compressor.


    What doe's the winner get??

  7. #7
    mwangi's Avatar
    mwangi Guest

    Re: Compressor run for 3 mins then off for 10 mins

    hi,if the fridge has a low pressure cut out then we have an under charge if not the compressor is overloaded or the filter drier is partially blocked. try flushing your system

  8. #8
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Compressor run for 3 mins then off for 10 mins

    So much attention to a trifle problem - just look where circuit breaks: that's it (then think a little - why). Let this thread's originator get used to a voltmeter also.