    chiller unloading



    hi all I have chiller type ALRHAST455.4 the chiller is controled by microtech (McQUAY) when the chiller start normaly & then the comp. loading is 100% the water temp. 34c the temp. setting is 10c.
    any advice please.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    70
    Posts
    4,700
    Rep Power
    47

    Re: chiller unloading

    Your LP and HP settings are?
    liquid line temp etc etc.
    Give us some details so we can help you jebar!
    Grizzly

  3. #3
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: chiller unloading

    what is infact yore question??

    Ice

  4. #4
    shiyam's Avatar
    shiyam Guest

    Re: chiller unloading

    Quote Originally Posted by jebar View Post
    hi all I have chiller type ALRHAST455.4 the chiller is controled by microtech (McQUAY) when the chiller start normaly & then the comp. loading is 100% the water temp. 34c the temp. setting is 10c.
    any advice please.
    ===reply shiyam from uae} you did not write 34 c, leaving or return water( temp)clearly. so when the leaving water temperature 34c better one more chiller. so you should understand and lean unloading loading chilled water temperature point.
    thank you
    shiyam...(mshiyam88@yahoo.com)

  5. #5
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: chiller unloading

    As others have stated your post is not clear .
    If you are saying when your chiller starts the water circuit temperature is 34c and the chiller set point is 10c, whether it is leaving or return water temperature is irrelevant as either way you are 24c above set point.
    At 24c above set point i would expect the loading to be 100%
    You need to clarify your post and give us more information .
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: chiller unloading

    A really old post.
    But generally chiller are controlled on return water temp., so set point +10'C , split 5.5'C leaving water at +4.5 'C .

  7. #7
    Join Date
    Sep 2009
    Location
    Cyprus
    Age
    65
    Posts
    110
    Rep Power
    15

    Re: chiller unloading

    and of course this 5.5C ΔΤ depends on the pressure drop across the evaporator DP

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  3. Absorption Chiller VS Mech. Chiller
    By Intern in forum Industrial
    Replies: 20
    Last Post: 30-05-2009, 08:31 AM
  4. york chiller motor rotation error
    By cesarnino in forum Trouble Shooting
    Replies: 7
    Last Post: 13-12-2008, 03:43 PM
  5. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •