Thread: Daikin new PCB board
-
17-06-2009, 11:59 AM #1
Daikin new PCB board
Just replaced new PCB board on a R22 RYP250B7W1, getting a UA fault, both boards are exactly the same. Do i need to get a jumper cable to set capacity on new board? wot connection does it go into is it X26a??
-
17-06-2009, 04:24 PM #2
Re: Daikin new PCB board
Swapped new PCB board with an old one from a identical unit in the same building, still got UA fault. I disconnected the remote cable from last unit on the line and the fault cleared. How can i get the number of units connected to a individual remote, surely there is a service setting which displays the number of units, the remote is a BRC1C51/61
-
17-06-2009, 06:39 PM #3
Re: Daikin new PCB board
Hi,
Sounds like you have a twin, triple or double twin system. This means you have either 2, 3 or 4 indoor units to one outdoor unit.
You need to programme the indoor unit as follows;
11-0-02 for twin systems (2 indoor units)
11-0-03 for twin systems (3 indoor units)
11-0-04 for twin systems (4 indoor units)
Hope it helps
Obi Wan
-
17-06-2009, 11:26 PM #4
Re: Daikin new PCB board
you got it obi wan!
champion!
-
18-06-2009, 07:11 PM #5
Re: Daikin new PCB board
Sorry Obi silly question how do you program the indoor unit, i dont recall seeing any dip switches relating to number of indoors. Its a twin system by the way.
-
18-06-2009, 11:35 PM #6
Re: Daikin new PCB board
Some how I knew you were going to ask that
OK
1, press the test button on the remote controller for 5 sec
2, then press the temp up button until you read “setting 11”
3, then press the timer down button until you read “0-02”
4, press the conformation button once (from the test button, up one, then one to the right)
5, finally press the test button once. You should see “88” for a few seconds.
Job done.
Good luck
Similar Threads
-
Daikin RZP1450V1 Main Board
By Lumpy2 in forum Trouble ShootingReplies: 1Last Post: 03-06-2009, 09:59 PM -
Daikin Inverter board failures
By Greengrocer in forum Air ConditioningReplies: 10Last Post: 21-05-2009, 04:35 PM -
Daikin Inverter Board / Compressor issues
By Greengrocer in forum Air ConditioningReplies: 12Last Post: 21-04-2009, 10:12 PM -
Daikin VRV wiring adapter board
By mchild in forum Air ConditioningReplies: 6Last Post: 24-11-2008, 11:02 AM -
Trane Defrost Control Board Energize "W" in cooling
By jcmorris2 in forum Heat PumpsReplies: 6Last Post: 02-06-2007, 03:40 AM