    mitsi condensor fan



    hey fellas took over a job today from another engineer who has just changed the reversing valve,i was the one who got to run it up pressure test vac etc etc.Ran the unit up found power going to the solenoid valve which there shouldnt be thus making it go into heat mode i checked the several other units next to it which are the same. So what makes power now go to the solenoid??? next problem was the condensor fan only running very very slowly and very jerky as if power spikes going to it??.I changed the fan with another unit and also the module but still the fan wouldnt run correct going to change the boards over tomoz and see were it takes me. What controls the fan from the board there is a connector,black and white then from the module a red and orange cable??? then fan had no power in it i could even stop it with my hand very easily thanks alot

    adam

    Mitsubishi electric

    Model No- PUH-P3YGAA
    R407C


    ajj

  2. #2
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: mitsi condensor fan

    sounds like you have a faulty board and the relay that supplies the 4 way valve is latched...

  3. #3
    Join Date
    Feb 2007
    Location
    north west
    Age
    36
    Posts
    244
    Rep Power
    18

    Re: mitsi condensor fan

    cheers brunstar turned out to be the board thanks alot

    adam
    ajj

Similar Threads

  1. Mitsi City Multi
    By SatPro in forum Trouble Shooting
    Replies: 4
    Last Post: 25-01-2010, 04:43 AM
  2. Mitsi Heavy Fault
    By coolments in forum Air Conditioning
    Replies: 2
    Last Post: 22-09-2008, 09:18 AM
  3. Mitsi Electric RP6AA Pump Fault
    By gwilliamson in forum Air Conditioning
    Replies: 8
    Last Post: 15-08-2008, 05:59 PM
  4. Mitsi Lossnay Heat Exchanger
    By sinewave in forum Air Conditioning
    Replies: 9
    Last Post: 05-02-2008, 06:55 PM
  5. Mitsi Problems
    By Latte in forum Air Conditioning
    Replies: 9
    Last Post: 12-02-2005, 08:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •