    Daikin new PCB board



    Just replaced new PCB board on a R22 RYP250B7W1, getting a UA fault, both boards are exactly the same. Do i need to get a jumper cable to set capacity on new board? wot connection does it go into is it X26a??



  2. #2
    Join Date
    Jan 2005
    Location
    Ireland
    Age
    43
    Posts
    111
    Rep Power
    21

    Re: Daikin new PCB board

    Swapped new PCB board with an old one from a identical unit in the same building, still got UA fault. I disconnected the remote cable from last unit on the line and the fault cleared. How can i get the number of units connected to a individual remote, surely there is a service setting which displays the number of units, the remote is a BRC1C51/61

  3. #3
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daikin new PCB board

    Quote Originally Posted by ronaldo9 View Post
    Swapped new PCB board with an old one from a identical unit in the same building, still got UA fault. I disconnected the remote cable from last unit on the line and the fault cleared. How can i get the number of units connected to a individual remote, surely there is a service setting which displays the number of units, the remote is a BRC1C51/61

    Hi,

    Sounds like you have a twin, triple or double twin system. This means you have either 2, 3 or 4 indoor units to one outdoor unit.
    You need to programme the indoor unit as follows;

    11-0-02 for twin systems (2 indoor units)
    11-0-03 for twin systems (3 indoor units)
    11-0-04 for twin systems (4 indoor units)

    Hope it helps

    Obi Wan

  4. #4
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin new PCB board

    you got it obi wan!
    champion!

  5. #5
    Join Date
    Jan 2005
    Location
    Ireland
    Age
    43
    Posts
    111
    Rep Power
    21

    Re: Daikin new PCB board

    Sorry Obi silly question how do you program the indoor unit, i dont recall seeing any dip switches relating to number of indoors. Its a twin system by the way.

  6. #6
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daikin new PCB board

    Quote Originally Posted by ronaldo9 View Post
    Sorry Obi silly question how do you program the indoor unit, i dont recall seeing any dip switches relating to number of indoors. Its a twin system by the way.

    Some how I knew you were going to ask that

    OK

    1, press the test button on the remote controller for 5 sec
    2, then press the temp up button until you read “setting 11”
    3, then press the timer down button until you read “0-02”
    4, press the conformation button once (from the test button, up one, then one to the right)
    5, finally press the test button once. You should see “88” for a few seconds.

    Job done.

    Good luck

Similar Threads

  1. Daikin RZP1450V1 Main Board
    By Lumpy2 in forum Trouble Shooting
    Replies: 1
    Last Post: 03-06-2009, 09:59 PM
  2. Daikin Inverter board failures
    By Greengrocer in forum Air Conditioning
    Replies: 10
    Last Post: 21-05-2009, 04:35 PM
  3. Daikin Inverter Board / Compressor issues
    By Greengrocer in forum Air Conditioning
    Replies: 12
    Last Post: 21-04-2009, 10:12 PM
  4. Daikin VRV wiring adapter board
    By mchild in forum Air Conditioning
    Replies: 6
    Last Post: 24-11-2008, 11:02 AM
  5. Trane Defrost Control Board Energize "W" in cooling
    By jcmorris2 in forum Heat Pumps
    Replies: 6
    Last Post: 02-06-2007, 03:40 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •