The pipe of the split A/C installation
How long minimal and the maximum of the pipe of the split A/C installation measurement 1 pk?
-
18-06-2009, 12:24 PM #2
Re: The pipe of the split A/C installation
Different systems have different lengths.
There is no minimum but the maximum can
vary from 15mtrs to 25 mtrs.
Each system will have an instruction book and in that book you will find the maximum length and how much refrigerant you need to add over a certain amount.
taz.
-
18-06-2009, 12:38 PM #3
Re: The pipe of the split A/C installation
Oil will return to compressor, when long the pipe until 25 metre, taz?
-
18-06-2009, 02:22 PM #4
Re: The pipe of the split A/C installation
as per installation instructions. It varies, so the manufacturers tell you with their specific units in the install instructions. The bigger the unit, the longer the run allowed as a general rule.
small 2kw units are normally 7m larger splits are up to 15m.
As far as oil return, that's mainly an issue if the outdoor unit is above the indoor unit and the pipes are exceedingly long.Last edited by paul_h; 18-06-2009 at 02:24 PM.
-
18-06-2009, 08:41 PM #5
Re: The pipe of the split A/C installation
-
18-06-2009, 11:33 PM #6
Re: The pipe of the split A/C installation
Oil return can be a problem, also pressure drop over the longer distances, but a good quality, well installed system will work well as long as it is within the peramiters set by the manufacture.
Yep good point
Some systems do have a minimum distance and I was being too general.
Cheers taz.
Similar Threads
-
Pipe Installation
By Rodders in forum Air ConditioningReplies: 5Last Post: 08-06-2009, 12:37 AM -
Installation question split system
By jom2000 in forum Air ConditioningReplies: 6Last Post: 16-05-2009, 01:17 PM -
Mitsi split freezing HP pipe
By Bat in forum Air ConditioningReplies: 8Last Post: 13-05-2008, 12:01 AM -
Q: Piping installation for Split Types
By brianubaldo in forum RefrigerantsReplies: 11Last Post: 30-04-2008, 02:23 PM -
Split System max pipe run length?
By fridge doctor in forum Air ConditioningReplies: 4Last Post: 18-08-2007, 01:14 AM