17-06-2009, 09:23 AM #1
Heat pump
hi Guys I have a Daiken consol heat pump. At the back of the outdoor unit there is a black stain on the ground. If this is refrigerant leaking how do I tell when it should be repaired and recharged? Does the heating suddenly stop and turn cold or does the heat slowly drop off over a period of time? It is difficult to know if the heater efficiency is similar to when the pump was first put in.
-
17-06-2009, 03:57 PM #2
Re: Heat pump
the stain is proably the oil that leaked out with the gas, get a qualified engineer out to it, he will tell you.
-
17-06-2009, 07:17 PM #3
Re: Heat pump
You are in New Zealand, so I assume you are having your cold season now and the system is used to provide heat, yes?
Most likely, the damp patch you can se is condensate that formed on the outdoor coil (that will be an evaporator or cooler now).
If you put some tissue paper down and let it soak up the damp (might be for a couple of hours whilst the system is running), can you set fire to it afterwards? (OK, REMOVE IT TO A SAFE PLACE BEFORE YOU TRY).
If what you can see is oil, it will burn easily, if it's water...
-
17-06-2009, 09:00 PM #4
-
17-06-2009, 10:46 PM #5
Re: Heat pump
how old is the unit? where in relation to the unit is the mark?
-
18-06-2009, 03:27 AM #6
Re: Heat pump
-
18-06-2009, 03:44 AM #7
Re: Heat pump
This is what I see at the rear of the outside unit
-
18-06-2009, 03:59 AM #8
Re: Heat pump
Yes it's winter and don't want to loose heat at an inconvenient time if it can be prevented with a timely call to a service man. The unit is not sitting level on it's platform and I will level it up when it needs to be overhauled as the piping will have to be loosened to do this. hence the question does it slowlyyyyyyyyy loose efficiency or is it "there today and gone tomorrow".The tissue trick showed it to be water and dry oil.
-
18-06-2009, 04:45 AM #9
Re: Heat pump
I'd say that, judging from the picture, you have a refrigerant/oil leak.
Performance will often gradually drop off until a critical minimum value is reached, after which you will really feel the difference.
Best to have a repairman come over, recover gas, leak-test, repair as required, re-charge gas - perhaps some additional oil, as required. The manufacturer may advise on a recommended service regimen.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
20-06-2009, 10:25 PM #10
Re: Heat pump
Thanks guys "a stitch in time saves nine"
Similar Threads
-
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
Heat pump hot water system
By kiamaian in forum Technical SpeculationsReplies: 4Last Post: 16-06-2009, 06:48 AM -
Homemade Heat Pump...
By AC_Hacker in forum New to REReplies: 0Last Post: 29-04-2009, 11:30 PM -
Pool heat pump water side diagram
By nike123 in forum Heat PumpsReplies: 23Last Post: 22-03-2009, 07:42 PM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM