    Economiser port



    Dear all,

    I have a problem with howden screw compressor, My problem is the economiser port gets red hot.

    I had connected the oil line from oil separator to the economiser port.

    The refrigerant is ammonia.

    Can any one suggest what is the reason for this and how to solve this problem.

    regards, and thanks in advance.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Economiser port

    Don't know this compressor or your pipe layout but it sounds as though hot gas is coming straight back to the compressor.

    Is the oil return line cool, warm or hot?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17

    Re: Economiser port

    Oil line is warm

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: Economiser port

    Have seen this on other machines also .

    I think its same gas being recirculated in and out of this port , so gas is getting more and more superheated .
    If oil return is not returning this will happen especially on VFD units when at low speeds .

    Best is return it into suction if possible .

  5. #5
    Join Date
    Mar 2006
    Location
    Philippines
    Age
    53
    Posts
    124
    Rep Power
    19

    Re: Economiser port

    What is the type of your oil cooler? Oil temp? Oil pressure? discharge pressure?
    If I'm not mistaken the pressure in economizer port is the pressure between your suction & discharge pressure.
    Make sure your oil pressure is higher than economizer port.

  6. #6
    Join Date
    Jan 2009
    Location
    INDIA
    Posts
    40
    Rep Power
    0

    Re: Economiser port

    Quote Originally Posted by Rajkumar View Post
    Dear all,

    I have a problem with howden screw compressor, My problem is the economiser port gets red hot.

    I had connected the oil line from oil separator to the economiser port.

    The refrigerant is ammonia.

    Can any one suggest what is the reason for this and how to solve this problem.

    regards, and thanks in advance.
    I think you have connected secondary oil seperator , coalescing element , drain to economiser port. In my view , you must connect it to suction line with restriction orifice in between so that pressure can be equalised to suction line. Hope this solves your problem. Orifice must be sized for the required pressure drop.

Similar Threads

  1. extra expansion valve and dryer port
    By CoolWell in forum Fundamentals
    Replies: 8
    Last Post: 07-10-2008, 03:10 AM
  2. Understanding Balance port TX valves
    By Mobbsy in forum Technical Discussions
    Replies: 12
    Last Post: 23-07-2008, 04:32 AM
  3. Looking for a source for stainless side port distributor
    By 128cyclist in forum Technical Discussions
    Replies: 1
    Last Post: 21-06-2007, 10:07 PM
  4. Problematic Economiser
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 9
    Last Post: 22-07-2005, 04:06 AM
  5. Balanced port TEVs
    By Prof Sporlan in forum Fundamentals
    Replies: 22
    Last Post: 25-02-2002, 03:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •