    I have four refcomp screw compressors with unloading issues. I can load or unload approx to 50% then after that point the slide moves to 100% and then wont unload. The solenoids move quite freely (load/unload)to 50% then tighen a little over this. Any ideas as I understand this is a common problem with these in europe? To remove these for overhauls will cost because of the skid location. All the solenoids have been checked and operate fine.

    Thanks for taking time out to look and answer this.

    Regards Conan
    conan.smith@cowleyrefrigetaion.com a hastie company.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Refcomp Screw Unloading problems

    Quote Originally Posted by GordonRefrig View Post
    I have four refcomp screw compressors with unloading issues. I can load or unload approx to 50% then after that point the slide moves to 100% and then wont unload. The solenoids move quite freely (load/unload)to 50% then tighen a little over this. Any ideas as I understand this is a common problem with these in europe? To remove these for overhauls will cost because of the skid location. All the solenoids have been checked and operate fine.

    Thanks for taking time out to look and answer this.

    Regards Conan
    conan.smith@cowleyrefrigetaion.com a hastie company.
    Hi Conan
    Can you say what model the screws are as I may be able to help!
    Basically when you checked the solenoid valves did you disturb the plates and gaskets beneath their housings.
    Because the way they are assembled dictates how they operate and as to which load capacity option they employ!
    Your issue is with the solenoids we just need to confirm what is happening?
    Grizzly

    Ps do you have 3 solenoid assemblies as 1 of them is the 75% load option .
    I suspect that is the one with the problem?
    Last edited by Grizzly; 17-06-2009 at 10:22 PM.

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Refcomp Screw Unloading problems

    hi as said before your problem is with the solenoides and gaskets verify correct instalation

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Refcomp Screw Unloading problems

    There is an inherent problem with early models: the slider has got a teflon scraper ring which seized more often than not. I've changed a number of those...
    It's a dirty job... all the oil has to be drained.

  5. #5
    Join Date
    May 2008
    Location
    Auckland
    Age
    44
    Posts
    7
    Rep Power
    0

    Re: Refcomp Screw Unloading problems

    Hi Conan

    Are we talking about Rivercity Casino Hamilton?

  6. #6
    Join Date
    Oct 2009
    Location
    USA
    Age
    67
    Posts
    28
    Rep Power
    0

    Re: Refcomp Screw Unloading problems

    Some things to check:
    1. If computor controled, recheck your settings on slide valve menu screen.
    2. Some slide valves have oil input or output metering device on each oil line. Check, if its too far open or closed.
    3. Use a voltage touch probe or equivalent to verify the coil is energize/ de-energize as needed.
    Good Luck.

  7. #7
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Refcomp Screw Unloading problems

    Hi, all

    unfortunately origin poster ... gone ... fishing, maybe check the date of the origin post ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  8. #8
    Join Date
    Jun 2010
    Location
    China
    Posts
    12
    Rep Power
    0

    Re: Refcomp Screw Unloading problems

    Here's a bit of history and contacts if you need them.

    RefComp and Thermokey form together the RTH group which is an independent group which has one owner who is the original founder Mr. Candio.
    RefComp makes the very same screw and piston compressors at their factories both near Vicenza in Italy and in Shanghai in China while Thermokey makes many types of heat exchangers for Air Con, Refrigeration , Process Control, Close Control , Power and Energy and Solar Energy markets and manufactures in Italy , China and Brazil.

    About 30 years ago Mr. Candio used to own Artec (heat exchangers) which he after sold to Alfa Laval. After RefComp was then founded and was a pioneering company with screw compressor technology specifically designed for HVAC and Refrigeration applications. During this past century Bitzer used to sell the large RefComp screw compressors through their sales network because back then they did not manufacture yet this kind of new screw compressor.
    After Thermokey was then founded. Nowdays Thermokey is pioneering in large aluminium microhannel heat exchangers specifically designed for HVAC and Refrigeration applications

    you can contact them at :

    sales@refcomp.it
    sales@thermokey.it

Similar Threads

  1. VSD on screw machines
    By Mike Hopkins in forum New Technologies
    Replies: 14
    Last Post: 20-02-2011, 12:10 AM
  2. screw verses reciprocating compressor
    By ukram in forum Industrial Compressors
    Replies: 14
    Last Post: 18-05-2009, 01:06 AM
  3. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Replies: 18
    Last Post: 27-01-2009, 10:36 PM
  4. Replies: 7
    Last Post: 23-09-2008, 09:24 AM
  5. Mono or twin screw
    By Nirmalya in forum Industrial Compressors
    Replies: 43
    Last Post: 12-09-2006, 03:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •