    Hi all,

    York Model H2CE120A5OB

    We have been asked to quote for a replacement condensing unit for an Air Handling Unit bringing fresh air into a hospital theatre.
    The current ducting draws in fresh air and either heats it through electric heaters or cool using an evaporator.

    The current twin compressor condensing unit on R22 has failed. The problem is does anyone know it duty? Johnson Controls who now own York don't know!

    I can't quote unless I know some tech details on this unit.

    Please help!!!

    MrC
    Scotland



  2. #2
    Join Date
    Aug 2007
    Location
    Germany
    Posts
    36
    Rep Power
    0

    Re: YORK Condensing Unit What kW capacity?

    Does the compressor show the swept volume on the nameplate? This would help to estimate the cooling capacity, volumetric efficiency is approximately 0.7.
    RTFM always thoroughly!
    Vacuum sucks!
    Sience rules!

  3. #3
    Join Date
    Jul 2007
    Location
    nr Carlisle
    Posts
    6
    Rep Power
    0

    Re: YORK Condensing Unit What kW capacity?

    I didn't check that as I hoped the make and model would have been sufficient.
    Unfortunately the job is about 50 miles away and I'd rather not have to return.
    MrC

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: YORK Condensing Unit What kW capacity?

    Or, what is the duty of the air handling unit ?

    edit: Found this, it's close but not quite the same.
    Equipment List
    Unit # Equipment Type
    1 CONDENSING UNIT YORK H2CE-120-A2SE NGJM091343 10TR 2000
    1 A AIR HANDLER YORK K3EU-120-A33B NBEF003270 10TR 2000
    Last edited by Brian_UK; 16-06-2009 at 10:53 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jul 2007
    Location
    nr Carlisle
    Posts
    6
    Rep Power
    0

    Re: YORK Condensing Unit What kW capacity?

    There aren't any details on the ducting and the evap is just a large finned coil about 26" x 48" x 6"
    Does the 120 in the model number mean 120kW?

    MrC

  6. #6
    Tassajara's Avatar
    Tassajara Guest

    Re: YORK Condensing Unit What kW capacity?

    I think that means 120,000 btu's based on the model number and that coil size. But that is only guess really i am bored stupid at the office. this site is the only thing thta kept me from killing myself today ;-)

Similar Threads

  1. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 07:25 AM
  2. Daikin ER8DWL condensing unit
    By al in forum Air Conditioning
    Replies: 5
    Last Post: 07-01-2009, 12:51 AM
  3. l'unite hermetique R12 Condensing unit
    By airefresco in forum Commercial
    Replies: 13
    Last Post: 08-02-2008, 10:08 PM
  4. TXV sizing with a larger condensing unit
    By kengineering in forum Technical Discussions
    Replies: 13
    Last Post: 27-08-2007, 10:44 PM
  5. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •