    Carrier chiller 30 hg starter gaurd fault



    Hi all could any one help regarding the above the chiller keep s coming up with starter gaurd alarm,
    The chiller cycles alot due to poor load, i think this is a antirecycle protection is this correct???

    thanks

    mariobros



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Carrier chiller 30 hg starter gaurd fault

    Can't find any reference to 'Starter Guard' in the manuals, what is the alarm code?

    Manual here if you want one....
    http://eto.carrier.com/lit.asp
    select 30HG and 'all'
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2005
    Location
    uae
    Posts
    54
    Rep Power
    19

    Re: Carrier chiller 30 hg starter gaurd fault

    Hi,

    Check your cc heater

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Carrier chiller 30 hg starter gaurd fault

    did you do any mesurments at all ???
    presure - temps - time - etc.ect.. ?

    Ice

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Carrier chiller 30 hg starter gaurd fault

    Are we going to hear from him again ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Carrier chiller 30 hg starter gaurd fault

    as mentioned before check your oil heater .the start guard monitores this
    if all else failes switch a startguard card from a near compressor .to verify its operation and if needed buy a new one it is not that expensive
    in order to reset a start guard .u need to turn off the power supply to the start guard
    this is only if u messured your currents and compressor parameters and found all ok

  7. #7
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Carrier chiller 30 hg starter gaurd fault

    I doubt it, just another 1 post wonder

  8. #8
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Carrier chiller 30 hg starter gaurd fault

    crank heater or sensor fault

  9. #9
    Mariobros's Avatar
    Mariobros Guest

    Re: Carrier chiller 30 hg starter gaurd fault

    Thanks all sorry for no reply dont get on here much got some good info from link posted

    Have a good week all

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. carrier chiller fault codes
    By al in forum Air Conditioning
    Replies: 7
    Last Post: 20-07-2009, 10:10 PM
  3. Carrier 30hwa chiller a207 fault
    By glenns in forum Trouble Shooting
    Replies: 1
    Last Post: 21-11-2008, 06:02 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •