Results 1 to 17 of 17
    Sep 2003
    54
    R502 Replacement.
    Got a Frozen Food Coldroom on R502 which due to leak on remote condensor has lost gas.
    A company has been previous to my visit but no gas ID label is on unit. Exp valve is R502 so I will have to assume that R502 is what is in the system. Customer does not recall what engineer did on previous visit.
    If I use R404A what oil do I need and do I need to do anything with expansion valve i.e orifice size (not sure of size at mo)?
    Or is there another gas I could use that involves no oil change and minimal adjustments R407A for example?
    Sep 2003
    ISRAEL
    72
    4,248
    Re: R502 Replacement.
    Hi lucas.
    Personally, now adays I don't like the retrofits.
    With 404A you need to use POE oil.
    For flushing Contact your refrigerant supplier.
    Capacity don't change but you have to install new TEV for 404A - the same capacity.
    As oil and dirt stays at the bottom of the receiver. It need to be replaced and of course 404A compressor.
    Pressure controlls will have to be re adjusted.
    Good Luck
    Chemi
    Jun 2002
    628
    Hi lucas
    Just to expand on chemis valid points Retrofitting is the way to go long term.However FX10 (R408A) will drop in the place of R502 with minimal problems,Available from HRP etc.( phase out period applies).
    Best regards
    Mark
    Jan 2003
    East Anglia
    1,160
    Hi Lucas,
    As Mark says, R408A is the short term drop in replacement and i have used in on loads of occasions and works fine.
    At the end of the day to convert to R404 is going to cost and with the age of the equipment is it really worth it. I have so far never conveted a unit to 404 purely because of the cost compared to the short term life of that age of a unit. Either scrap the whole unit & but a new more reliable one or just use 408
    Raymond
    5,667
    Why can't you have a look at the last engineers report sheet to see what work he carried out on the system? Surely the customer should have a copy?
    Apr 2001
    2,099
    27
    Use Drop In Isceon R69 or R403B
    Sep 2003
    54
    No report history available otherwise I would of read it.
    Thing that amazes me is that the unit is not even labeled for R502 nor are there any signs of labels being removed. Just cannot understand why people cannot take time to label things!
    Will suggest customer has to look at new equipment but for now go for the drop in option. Unit at least 12-15 yr old so cost has to be a factor here, so as ever it is up to the customer and as usual they will go for cheapest option of course guaranteed.
    Jan 2002
    Long Beach Ca
    48
    47
    stateside 502 replacement most common now is 507 , poe retro, same valve most applications
    Jun 2001
    Gloucestershire
    13
    Hi Lucas,
    Why don't you try ISCEON 79 its not HCFC based like R408A but it can be used with same oil type that is in system.
    Peter
    Aug 2004
    Holland
    55
    For the rare occasion where we encounter R502 and have to change to the refrigerant, we use HP 80 = R402a just drop in, no oil or tev change, works perfect, in holland is is a gas witch will be phased out in future.
    BTW wats wrong with selling a new and modern installation.
    Regards Victor
    Dec 2001
    nottingham
    96
    FX10 works well as a drop in, just remember to charge system to correct operating pressures, i have found systems in the past charged to a full sight glass have been way over charged
    Jun 2004
    Wirral UK
    58
    68
    R402a R402b R403 R408a Are all pretty much the same in the feild in my experience. Depending on the size of the system if it is quite small I would advise the customer to prepare himself to pay for the cost of a new system in the next couple of years. If however it is larger I would sugest looking at changing it over to a longer term replacement. I recently was involved with a R502 Blast Freezer that had been changed over to R22 by company policy and then changed over to Isceon 59(R417a) It works really really well and out performs it's 25 year old design spec. It is quite a big blast freezer though.
    "It's better to remain silent and be thought a fool than open ones mouth and remove all doubt"
    Apr 2002
    Hamilton, Canada
    58
    why would someone want to use HP80. too high of a discharge pressure, causes allot of gtief in the summer time with high head problems, anything i service that was 502 and now HP80, needs a sprinkel on the condenser in summer
    go to 404 or 507 (less glide) and POE oil, no need to change TEV
    Nov 2007
    Stan
    In the west cost R-507 is popular
    In the east cost R-404A is popular
    most supply hoses dont carry more then 3 to 4 jugs of R-507
    70
    4,700
    47
    Quote Originally Posted by yoelyeve View Post
    Stan
    Have you noticed the dates on these posts.
    I doubt you are going to get relevant replies!
    Nov 2007
    Shaun
    I have 4 Ice cream plant's running on R-408A and I'm getting better performance then R-404A by about 6% even on a 95F day
    Box temp About -22F
    Dont need no sprinkler
    Nov 2005
    New Zealand
    550
    Shaun
    Box temp About -22F
    This thread iis over 6 years old
  1. R 417 A direct replacement of R 22
    By abbasi in forum Refrigerants
    Last Post: 08-09-2011, 12:47 AM
  2. Replacement stat
    By Lucas in forum Domestic
    Last Post: 02-08-2006, 11:28 PM
  3. R-22 replacement
    By shogun7 in forum Refrigerants
    Last Post: 26-07-2004, 07:57 AM
  4. F 11 replacement for flushing
    By andrewuk in forum Refrigerants
    Last Post: 17-10-2003, 11:03 PM
  5. Best refrigerator, R22 or r502
    By AndrOvr in forum Refrigerants
    Last Post: 08-07-2003, 03:51 PM