We installed a 7kW Compact Fujitsu cassette a few weeks ago.
Within a week there was complaints that the unit was dripping the odd droplet of water on to the desk below.
Went back today to investigate further.
Upon investigation all seemed well with the unit but on watching the unit over 30 mins or so it could be seen that the fan was blowing droplets of water off the coil before they had dripped in to the tray and out through the louvers.
The tray is centraly located OK but does seem rather close to the edge of the coil.
Am waiting for Fujitsu to get back to me on this one.
Anyone any ideas?
Just wondering if it could be due to the design as they've crammed 7kW of duty in to a standard 600mm ceiling tile space?
He who dies with the most Toys, WINS!
-
15-06-2009, 09:19 PM #2
Re: Spitting Cassette!
Probably a silly question but is the cassette level?
The difference between genius and stupidity is that genius has its limits.
Marc
-
15-06-2009, 09:52 PM #3
Re: Spitting Cassette!
Yes it is marc.
It does it after only 5-10 mins on cooling before the tray has even had chance to partialy fill.
As stated it seems to be blowing off the coil before it even hits the tray.He who dies with the most Toys, WINS!
-
15-06-2009, 10:14 PM #4
Re: Spitting Cassette!
Does it happen on low speed fan as well as high ?
I presume it is a normal office application not high humidity and the sizing of the system is correct.
-
15-06-2009, 10:21 PM #5
Re: Spitting Cassette!
No andy it seems OK on a lower Fan speed as this is what I did initialy as my first visit was a late afternoon flyer.
Office is L shaped and the other side is not conditioned yet (but will be after other building works) so yes technicaly the unit is undersized at the mo.
All that aside this has never happened before in simlar circumstanceHe who dies with the most Toys, WINS!
-
15-06-2009, 10:24 PM #6
Re: Spitting Cassette!
Could it be ice and not condensate ?
-
15-06-2009, 10:29 PM #7
Re: Spitting Cassette!
No, I've stood and watched it off my steps with a maglite torch shining up the louver!
It's definately droplets of water driping off the edge of the tray and out of the louver.
Stripped it down today, tray out everything to see if the tray way miss-aligned or sumat, but no all was fine.
He who dies with the most Toys, WINS!
-
16-06-2009, 07:08 AM #8
Re: Spitting Cassette!
If I was you I would get on to Eurofred and ask them to come to site or replace the cassette, I know what you mean about the tray been close to the edge of the evaporator though, I have noticed that myself.
-
16-06-2009, 07:29 AM #9
Re: Spitting Cassette!
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
16-06-2009, 08:50 AM #10
Re: Spitting Cassette!
I have experienced the same problem, it is a design fault, if i can recall there is no gap between the pan and the coil on two corners Fujitsu have crammed a 7kw coil in a 5kw pan.
The condensate runs down the coil and on to the top lip of the pan instead of into it.
It really is that simple guys!!!
-
16-06-2009, 08:12 PM #11
Re: Spitting Cassette!
Not been back to site yet PP and I've had a few pointers of another of our learned friends on here.
What was the outcome of your situation with Fujitsu?
I've not actualy managed to speak to them yet as their Tech line is generaly un-maned most of the time and all U get is an answer phone!He who dies with the most Toys, WINS!
-
17-06-2009, 08:23 AM #12
Re: Spitting Cassette!
According to Fujitsu no one else has had a problem!!!!!
From memory I managed to wedge something between the coil and the pan about 9mm in thickness just to ease the pan away from the coil.
Job sorted.
Good luck mate
-
18-06-2009, 04:37 AM #13
Re: Spitting Cassette!
Are you sure the unit is not under charged?
If it is a long pipe run, was there refrigerant added?
-
19-06-2009, 11:50 PM #14
Re: Spitting Cassette!
i have seen a similar problem before on a new denco it had an oil film on it after it was degreased it was fine the water would not wet the coil and was blown off
-
23-06-2009, 07:19 PM #15
Re: Spitting Cassette!
UPDATE!
Fixed it!
With no help what-so-ever off Fujitsu Techline who seem to be permanently on answer phone!
It was exactly as PP stated, that the coil was touching the inside of the tray and therefore letting the fan blow beads of condensate along the edge of the tray till they get to an edge then fall off!
A few strategic 'Window fitting' plastic spacers sorted it out though!
Won't be fitting another 7kW Fuji cassette that's for sure!
Cheers PP!He who dies with the most Toys, WINS!
-
23-06-2009, 09:59 PM #16
Re: Spitting Cassette!
Well thats what you get for fitting cheap junk.... LG in future, eh?
Karl
-
23-06-2009, 10:03 PM #17
Re: Spitting Cassette!
Well at least I didn't have to rip it out, eh Karl!
He who dies with the most Toys, WINS!
-
23-06-2009, 10:12 PM #18
-
23-06-2009, 10:14 PM #19
Re: Spitting Cassette!
Give 'em a few weeks and they'll fall out on their own...
Karl
-
23-06-2009, 10:28 PM #20
Re: Spitting Cassette!
.....................
He who dies with the most Toys, WINS!
-
24-06-2009, 03:24 AM #21
Re: Spitting Cassette!
^ lol...
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
25-06-2009, 06:19 PM #22
Re: Spitting Cassette!
Hi guys , i think problems started when you bought Fujitsu. I gave them up in the nineties when their relays were found to be undersized on the indoor p.c.b.
think about useing Toshiba as an alternitive, i ve found them reliable.
-
25-06-2009, 07:37 PM #23
Re: Spitting Cassette!
That's all well & good Chill it but a Tosh Cassette is a huge amount more than a Fujitsu unit.
Tosh prices are on par with Mitsi & Daikin I believe so I may as well fit a Mitsi unit which I'd spec all day long if price was not key!
He who dies with the most Toys, WINS!
-
25-06-2009, 07:51 PM #24
Re: Spitting Cassette!
Sinewave, i recommend you give Tosh a try.
They are ultra reliable, easy to fit, and the back up is second to none.
For small guys like me, they are un-beatable ......and they are a little bit cheaper that Daikin and Mitsi, not much but a little bit.
Eggs
-
25-06-2009, 08:11 PM #25
Re: Spitting Cassette!
Might give em a go then, whose the best supplier in 'Middle England' then?
HRP?He who dies with the most Toys, WINS!
-
25-06-2009, 09:49 PM #26
-
25-06-2009, 10:07 PM #27
Re: Spitting Cassette!
Im a bit surprised about the Fujitsu comments, they are all I fit since my LG days and out of 50 units I had problems with 2, one was me over tightening a flare (purchased a torque spanner after that) and a couple of months ago an inverter board failed after 2 years so overall I have been very pleased with Fujitsu, decent value for money and I have confidence in the brand.
-
26-06-2009, 11:49 AM #28
Similar Threads
-
Gree cassette error?
By Andy AC in forum Air ConditioningReplies: 2Last Post: 11-07-2008, 09:23 PM -
Removing 1 cassette from a VRF
By marc5180 in forum Air ConditioningReplies: 5Last Post: 29-02-2008, 06:04 PM -
Daikin 7kW Cassette +supply duct to small office
By Makeit go Right in forum Air ConditioningReplies: 6Last Post: 12-12-2007, 03:41 AM -
LG Cassette lights
By Climateman in forum Air ConditioningReplies: 14Last Post: 27-03-2007, 05:55 PM -
LG Cassette
By Abe in forum Air ConditioningReplies: 16Last Post: 01-07-2005, 07:31 AM