Using 134a in R600a bottle cooler
Hello!
Does anyone with HFC experience know if I can 'drop in' 134a to a system which has been running on R600a and leaked to 0barg?
It seems the unit was designed for 'either or' from what I can gather, but i'm not sure about oil compatibility or hazards etc...
Thanks all, merry xmas.Last edited by Contactor; 14-06-2009 at 10:59 PM. Reason: grammar
-
15-06-2009, 03:15 PM #2
-
15-06-2009, 08:07 PM #3
Re: Using 134a in R600a bottle cooler
Contactor,
Use of R134a is not to be done in R600a model compressor for the following reasons:
1. Oil compatibility - as you guessed is an issue. 134a needs POE and R600a uses mineral oil
2. The pressures of R134a are almost double of 600a. chances of more leak as the system components might not have been tested at higher pressures by the manufacturer and also overloading and tripping of motor due to higher load on it.
3. Motor torque characteristics will be different for the relatively higher pressure 134a
4. Compressor displacement requirement for a required capacity for 600a is higher. So, 134a will overload and trip the motor.
Look at refrigerant properties to decide on retrofit refrigerants.
-
16-06-2009, 09:34 PM #4
Re: Using 134a in R600a bottle cooler
Thanks KR / Taz, very helpful.
Similar Threads
-
Bottle cooler tripping
By dunny123 in forum ElectricalReplies: 3Last Post: 20-06-2008, 10:20 PM -
r600a or 134a
By Minestrone Dave in forum RefrigerantsReplies: 16Last Post: 02-06-2008, 07:57 AM -
Bottle Cooler on Propane
By smpsmp45 in forum DomesticReplies: 0Last Post: 13-09-2007, 12:07 PM -
Bottle cooler
By Dave M in forum DomesticReplies: 3Last Post: 05-09-2007, 11:52 PM -
Quest bottle cooler
By Andy AC in forum CommercialReplies: 5Last Post: 24-06-2007, 11:32 AM