    Condenser Liquid Seal



    Have any of you ever had trouble maintaining one in a shell and tube condenser?
    How do you know if you have a good liquid seal?
    We have a system that has constant flash gas in the liquid line that we can't get to clear up. The system is 404a and it's supposed to be at 105condensing but even at 350psi (which is way overcharged) we can't supply clear liquid.
    The condenser water side operation seems ok and have checked everything else.
    http://www.refrigeration-engineer.co...ad.php?t=19004

    This is a Standard Refrigeration condenser and is rated at 500k btuh at the operating conditions, the system rejects aprox 300k btuh max.

    The liquid line is really hot which indicates the hot gas is going through the seal, any of you have experience with this?



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Condenser Liquid Seal

    Hi Chesybold
    Slightly off track here.
    But is there a liquid line filter before the sight glass.
    If there is what is the temperature difference across it?
    Grizzly

  3. #3
    Join Date
    Jan 2008
    Location
    USA
    Posts
    28
    Rep Power
    0

    Re: Condenser Liquid Seal

    No temp differance across liquid line filter. Sightglass before filter and another by txv valve

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Condenser Liquid Seal

    What temp is water in/out, what temp liquid after condenser, is it piped correctly?

    al

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Condenser Liquid Seal

    Where is the liquid line? And, how long is it?

    Does the liquid line flow up or down?
    If all else fails, ask for help.


  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Liquid Seal

    Quote Originally Posted by Chseybold View Post
    the system rejects aprox 300k btuh max.
    A detail you neglected to mention in the other thread.

    BTU = GPM x dT x 500

    300k = 40 x 15 x 500

    So, your dT would be 15 at max output.

    Your incoming water is 78F, so the water out would be 93F.

    Your approach is 32F.

    Add that to the water out temp and the SCT would be about 125F. The high side pressure would be about 331psi at max output.
    Last edited by Gary; 15-06-2009 at 03:41 PM. Reason: math corrections... duh

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Liquid Seal

    The approach is excessive. It should be no more than 20F. If it were 20F, the SCT would be about 113F, which would give you a high side pressure of about 280psi.

    So if the approach were reduced, the pressure would be 280psi.

    With a 60 GPM pump, the dT would be reduced by 5F, as would the SCT. The SCT would then be 108F with a pressure of 265psi.

    So, if all were well and the pump size were increased, you would have 265psi when the system was at max.
    Last edited by Gary; 15-06-2009 at 03:47 PM. Reason: More math mistakes

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Condenser Liquid Seal

    Seems my math was way off last night. I have corrected the mistakes in the above posts... that's what I get for posting at 2AM.
    Last edited by Gary; 15-06-2009 at 03:51 PM.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Condenser Liquid Seal

    Any water-cooled condenser I have seen operates with a condensing temperature no higher than 105°F, if it was designed properly.

    If the discharge pressure is too high and the system appears under-charged you most likely have a fouled condenser. That would give you high discharge pressure... and if the system appears under-charged you would have hot gas flowing down the liquid line.

    You need to provide some data on the condenser....

    Water flow
    Water temperatures in & out
    Condenser refrigerant outlet temperature
    If all else fails, ask for help.


  10. #10
    Join Date
    Jan 2007
    Location
    USA
    Age
    59
    Posts
    145
    Rep Power
    18

    Re: Condenser Liquid Seal

    I'm curious. How do you know you have flash gas? If the refrigerant flashes at the sight glass that doesn't mean that it's flashing before the valve. Did you torch the receiver? I started a five ton walk in freezer with 404 a and could not clear the sight glass even though the receiver was at fifty percent. When I asked our engineering department why it was flashing I was told that with the condensing unit on top of the box with 404a and a vertical liquid line once the refrigerant enters the s/g it will have a tendency to flash. I have been servicing and starting up supermarkets for years and this is the only unit I have seen do this on every occasion. Sometimes I don't try to figure everything just makes sure it works.

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Condenser Liquid Seal

    Quote Originally Posted by joe magee
    ...I asked our engineering department why it was flashing I was told that with the condensing unit on top of the box with 404a and a vertical liquid line...
    Hi Joe.

    Vertical liquid lines can cause flashing. The reason is due to static pressure. When the liquid flows up the static pressure decreases, which causes the liquid to flash due to the lower pressure. You need subcooling to overcome this.

    If the liquid flows down, the static pressure increases. Therefore the liquid stays in liquid form only.
    If all else fails, ask for help.


  12. #12
    Join Date
    Jan 2007
    Location
    USA
    Age
    59
    Posts
    145
    Rep Power
    18

    Re: Condenser Liquid Seal

    The liquid line coming from the receiver went down to the txv. I had 10 to 12 degrees of subcooling so I knew there was liquid. If you looked at the sight glass you could see the refrigerant rushing in. The s/g was halfway filled with refrigerant if that makes sense. My thinking was I should have a seal from the txv back to receiver. One of our engineers told me because the s/g was a larger diameter then the liquid line it would flash. Now I know that isn't always true, but in this case it was.

  13. #13
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Condenser Liquid Seal

    You can't always trust sight glasses for charging systems. I've seen them clear full, partially full, and with bubbles or froth. You have to keep this in context with what the system is doing also.

    If you are starting up a hot system, nothing is where it will be after the temperatures have stabilized. Sometimes systems have a mind of their own too...
    If all else fails, ask for help.


  14. #14
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Condenser Liquid Seal

    try checking pressure drop between compressor discharge & TXV.

    Exessessive pressure drop would possibly show these symptons i.e undersized liquid line!

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  4. Gas / Liquid ratio in Condenser
    By stesmith1981 in forum Technical Discussions
    Replies: 9
    Last Post: 11-04-2006, 08:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •