Carrier Air Cooled Chiller
Dear All,
We have 2 Carrier air cooled chillers 30 GTR070. both the units circuit B does not get commad to start from the processor board K5 relay. we presume the demand to start the other compressor is there as water temp is high. is their any configuration required, any help
thanks in advance
-
14-06-2009, 04:51 PM #2
Re: Carrier Air Cooled Chiller
However I do not know that Carrier, first that comes to mind is "system B off" on both chillers, maybe?
-
16-06-2009, 10:11 AM #3
Re: Carrier Air Cooled Chiller
i'm not sure about carrier chiller but maybe there's setting problem on both chiller. propably setting for compressor system B is off.
-
16-06-2009, 10:39 AM #4
Re: Carrier Air Cooled Chiller
are A compressors running ?
mmm to beer or not to beer...........lets drink breakfast
-
16-06-2009, 11:34 PM #5
Re: Carrier Air Cooled Chiller
Source for manual here...
http://eto.carrier.com/lit.aspBrian - Newton Abbot, Devon, UK
Retired March 2015
-
17-06-2009, 09:36 AM #6
Re: Carrier Air Cooled Chiller
lowcool yes Circuit A compressors are working. circuit B compressors does not get command to start even though there is a demand for cooling. this is same for both chillers.
Brain thanks for the link
sorry could not get any solution
-
17-06-2009, 01:53 PM #7
Re: Carrier Air Cooled Chiller
is the cooling demand output voltage from controller or indicator light,sounds like something either not commissioned properly or hi side coolling is not effective,im only a commercial fridgy and probably never seen what you got.sounds like this is first time problem,how old is plant.
mmm to beer or not to beer...........lets drink breakfast
-
19-06-2009, 11:45 AM #8
Re: Carrier Air Cooled Chiller
Lowcool
Circuit A is working fine
But Circuit B does not get any command to start. its is the case with both chillers
-
21-06-2009, 10:13 AM #9
Re: Carrier Air Cooled Chiller
sounds to me as if this chiller was not commisioned properly either there is a dip switch not on/off or control not set up correctly. it looks like it does not know there is a circuit B. If you take off a hp or lp transducer see if that brings up a fault and it is comunicating to circuit B. if you put the control in LOCAL ON will it stage up all circuits?
-
21-06-2009, 06:43 PM #10
Re: Carrier Air Cooled Chiller
someone being messing around whit the control panel ????
see if a complete factory reset helps. ceep a manual at hand for comparing in/outputs.
Ice
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
Refrigerant Temperature in the Water/Air Cooled Chiller
By jinx in forum FundamentalsReplies: 16Last Post: 19-02-2009, 11:43 PM -
Carrier Chiller Help
By superswill in forum Trouble ShootingReplies: 7Last Post: 18-01-2007, 10:06 PM -
Carrier chiller oil migration
By lowtech in forum IndustrialReplies: 5Last Post: 30-04-2006, 04:11 PM