    Question No power to outdoor unit



    Hello My name is Matt- I am an Ice machine engineer.
    A customer asked me to look at his cellar cooler. Indoor on and blowing unit reading 33 ambient in there i reckon. and set temp to cool was 4 ....outdoor unit no power to contactor -pushed contactor in nothing run . Does anyone think it could be the controller? should there always be power available to outdoor unit? a simple explanation of how the power is set up to bring condensing unit on and off would be really helpful please guys.
    Regards
    Matt



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: No power to outdoor unit

    If pushing contactor in doesn't run compressor, than you probably have power supply problem from main control board. It should always be voltage present on contactors power supply contacts.

  3. #3
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: No power to outdoor unit

    Whats, the sort of unit is it? If its a beer master, it will have separate supplies to the indoor and outdoor unit. Also will have no control wiring - works on pump down, liquid solenoid valve on indoor unit, when solenoid valve is shut outdoor unit runs until lp switch stops compressor.
    Sounds like you have no power to the condenser, possibly tripped mcb/rcd. If it has there is usually an expensive reason.

    Andy

  4. #4

    Re: No power to outdoor unit

    Thankyou
    love this Site! i think control board needs changing then right?

  5. #5

    Re: No power to outdoor unit

    That sounds right as after a few minutes I can hear a soleniod energising on indoor unit. and your right about RCD this is in a building in soho London and unit on roof with loads of other a/c equipment and not easy to find breaker board.
    Lot more wiser now thankyou

Similar Threads

  1. Power consumption of Chiller
    By adrian116 in forum System Optimization
    Replies: 7
    Last Post: 24-04-2009, 05:05 PM
  2. compressor ratings in horse power
    By themba in forum Fundamentals
    Replies: 6
    Last Post: 30-03-2008, 12:07 AM
  3. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM
  4. NEW 3-Phase IGBT Inverter Power IC
    By theberes in forum New Technologies
    Replies: 14
    Last Post: 01-03-2004, 01:10 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •