    mean temperature??



    When ,in heat load calculations,do we use temp diff as opposed to mean temp.? With coldroom wall loss applications we just use temp difference, but with heat exchangers we use the mean temp?

    Some formula :

    kw = a x u x temp difference

    kw = a x u x mean temp difference


    When would we use the two different calc's?
    Last edited by Drew; 14-06-2009 at 04:00 AM.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: mean temperature??

    Drew. It is called log mean temperature difference, abbreviated to LMTD, as the temp change is not linear, this will average as a mean change the difference.
    hope this helps. Magoo

  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: mean temperature??

    Quote Originally Posted by Drew View Post
    Why ,in heat load calculations, do we work with mean temperature differences as apposed to inlet and outlet temperature.

    Some formula :

    kw = q x u x temp difference

    kw = q x u x mean temp difference


    When would we use the two different calc's?
    Inlet and outlet temperature are temperatures refering to the same fluid as opposite of the logaritmic temperature difference.
    Inlet and outlet temperature can be used to get the heat received or released by the fluid > m.cp.(Tout-Tinlet) if you know their values.

    m.cp.(Tout-Tinlet) must be equal to U.A.LMTD if no phase change occurs. If phase change occurs you must sum this part to the sensible heat part.
    To make progress is never good enough, I want to do better and better and better

  4. #4
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    216
    Rep Power
    18

    Re: mean temperature??

    Thanks for the replies.

    I have given it some thought and with the help of your replies now understand that when we use the formula:

    Kw = a x u x LMTD it is for heat transfer through an item that doesnt have a constant temp diff and this is why we find an average.

    Kw = a x u x temp diff. This is used to find the heat transfer rate when the temp diff is constant. Loke a coldroom wall.?

    kw = kg/s x shc x temp diff. This is used to establish the heat gain or loss of a product.
    Last edited by Drew; 14-06-2009 at 08:58 AM.

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: mean temperature??

    An excellent academic reference book to get you going in the right direction:

    "Fundamentals of Heat and Mass Transfer", Incropera F.P., De Witt D.P., John Wiley & Sons

    Chapter 11 - Heat Exchangers, will provide you the info you are looking for.

    ------------

    For a condenser, the refrigerant side essentially comprises three sections - de-superheater, condenser, sub-cooler. These sections can theoretically be split up into 3 separate heat-exchangers. There are solid theoretical reasons for doing this. Each section has its own dTlm (log-mean temperature difference).
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 01-02-2009, 11:23 PM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •