    Troubleshooting a Manitowoc QY1304A, complaint of not making enough ice. Havests ice once every 15 minutes but only drops about 75% of the ice off the evaporator. The upper left quadrant doesn't get cold enough to freeze the water and has missing cubes. Is this a pressure issue? Another guy looked at it and said, "your evaporator is going bad and needs replaced".



  2. #2
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Lack of ice

    The condenser is clean, if cooled by air ? If by water, flow is good and filter is clean?

  3. #3
    suva134a's Avatar
    suva134a Guest

    Re: Lack of ice

    It's air cooled with a filter over the coil, and I just changed the filter to see if that changes anything. The filter was a little dirty, but there should have been plenty of air flow. I ran it without the filter and still noticed 25% of the evaporator without ice. I'm headed back to look at it again.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Lack of ice

    Short of gas, what are the suction and discharge pressures. If coil / HX is not flooded low ice volume. Some had those dodgy discharge by-pass valves to maintain liquid supply pressure from discharge to condenser outlet, if they go wild they can really screw things up. Check with a thermometer. If in doubt pinch it off with a pinch off tool and watch changes with pressures and coil flooding.
    Just a thought.
    Magoo

  5. #5
    Join Date
    Sep 2007
    Location
    United States
    Posts
    167
    Rep Power
    17

    Re: Lack of ice

    Look at top left corner of evaporator and see if any plastic is cracked. Next check for contact of evap coil pass to grid. Evaporator may have run with extra thick ice and expansion separated grid from coil. The evaporator can be replaced but check date of purchase both for warranty coverage and for age of unit. The repair often ends up no where near a factory job. Also be careful hooking up manifold with long hoses to system. ***** charge on an ice machine is critical for operation. I use a set of gauges connected to a short quick coupler to minimize ***** loss. Good luck. Call Manitowoc tech support. They are usually very helpful. Just have specs and temps on hand as listed in the pocket manuals. They will be asked for.
    Don't leave it like you found it.....Leave it like it should be !!!

Similar Threads

  1. HRP/NRS Parts Supplies (Lack of)
    By Latte in forum Chit Chat & Service Stories
    Replies: 25
    Last Post: 30-11-2008, 02:35 PM
  2. Lack Of Training Centres
    By Latte in forum Training
    Replies: 12
    Last Post: 06-11-2008, 02:56 PM
  3. Foster 1/3 Lack of airflow problem
    By Latte in forum The Trail of Tears
    Replies: 6
    Last Post: 14-08-2008, 11:49 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •