ice cream machine evaporating pressure
hello
i have a taylor 152-44 ice cream machine running on R404a. anyone know what the evaporating temperature should be
thanks
steve
-
11-06-2009, 02:08 PM #2
Re: ice cream machine evaporating pressure
18psi i used to use that for 502 cant be far off that
-
16-06-2009, 01:31 PM #3
Re: ice cream machine evaporating pressure
great thanks for that
regards
steve
-
09-10-2010, 03:40 PM #4
-
23-10-2010, 08:08 PM #5
Re: ice cream machine evaporating pressure
Don't understand why you want evap temp- to charge unit?
Never ever charge capilliry systems by temp or pressure, charge by weight. The charge weight is on the info plate on machine
Hope that helps
-
29-10-2010, 08:18 AM #6
-
31-10-2010, 11:26 PM #7
Re: ice cream machine evaporating pressure
I service many Taylor IC machines mostly in McDonalds...20psi suction is right on the money.
Paul Paxson
PAX Commercial Refrigeration
pawpax@verizon.net
"The early Bird get's the worm, But the second mouse get's the cheese"
-
03-11-2010, 09:02 AM #8
Re: ice cream machine evaporating pressure
someone had to charge the thing the first time to get the charge weight.
so if you design a system from scratch what do you do then champ???
a good refrig engineer will charge using subcooling and superheat as a guide to know what is going on, along sith sst and sct obviously....and she said "give it to me you big fridgie"
-
03-11-2010, 11:37 PM #9
Re: ice cream machine evaporating pressure
These systems (capilliry) are also called critically charged systems, that means the charge is critical. When designing these systems, manufacturers can test their equipment in lab conditions. They also work out the inside volume of the pipework, suction accumulator etc. If you over charge the unit, liquid will back up into the condenser, reducing the surface area, increasing the condensing pressure, in turn increasing the evap pressure and temp, wich means evap temp outside spec. If you under charge, high superheat, not enough cooling for compressor, heat kills compressors.
New F-GAS (EU) regulation also specifically states that all critically charged units must only be charged by weight.
I have never ever seen any manufacturer say in any off their manuals or info plates to charge a unit to a specific pressure.
The reason AC suppliers started precharging their units were all the comebacks from "Engineers" over charging the units.
Will probably get lots off replies telling me "I charge like that, never get problems"
Thats ok with me, I will always charge by weight. Will rather Google or call manufacturer to get charge weight.
-
06-12-2010, 01:16 PM #10
Similar Threads
-
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Benji
By benji in forum Trouble ShootingReplies: 29Last Post: 30-01-2008, 01:25 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM -
Cattabriga Ice Cream Machine
By Abe in forum Trouble ShootingReplies: 9Last Post: 26-04-2003, 01:06 PM