    Is R134A compatible with these equipments? Why and Why not? Any advice for retrofitting?
    1. reciprocating compressor
    2. DX evaporator
    3. Water cooled condenser (with cooling tower)
    4. Thermostatic Expansion Valve



  2. #2
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    331
    Rep Power
    17

    Re: system compatibility

    Quote Originally Posted by mjpaolo View Post
    Is R134A compatible with these equipments? Why and Why not? Any advice for retrofitting?
    1. reciprocating compressor
    2. DX evaporator
    3. Water cooled condenser (with cooling tower)
    4. Thermostatic Expansion Valve
    We're going to need more information. To start with, a compressor model number would help.

  3. #3
    Join Date
    Mar 2009
    Location
    Philippines
    Age
    35
    Posts
    16
    Rep Power
    0

    Re: system compatibility

    I'm sorry I don't know the compressor model. The engineers in charge of operating the ac system don't have the data anymore because it was lost already long time ago. This is just I know about the compressor. Reciprocating, 12 cyl, 4 unloaders, 125hp Motor, 1775 rpm, 220v, 312 MRA, 1973 LRA .

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: system compatibility

    The short answer is yes.

    But...
    Assuming that what you really want to know is if you can replace the refrigerant the system was designed for the answer will be NO.

    Someone with experience of these tasks needs to evaluate the system.

    Depending on what refrigerant currently in use, the pressures will change, the oil in the compressor will not be compatible, the seals might need replacing and so on.

    The TEVs are refrigerant specific and will need replacement as the gas are changed.

  5. #5
    Join Date
    Mar 2009
    Location
    Philippines
    Age
    35
    Posts
    16
    Rep Power
    0

    Re: system compatibility

    Thanks for the advice!
    I have this compressor which is really so old that I don't know its data and specifications.Can anyone give me a link on where to find compressor model no.?

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 02:03 PM
  3. Enthalpy Increasing Buffer System
    By Reflexive in forum Technical Speculations
    Replies: 3
    Last Post: 23-12-2008, 04:18 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •