    overcharge



    Had a chat today with another mechanic about diagnosing an overcharge. My question is - Is it possible to have a flashing sight glass if an overcharge exists?



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: overcharge

    Quote Originally Posted by SL82 View Post
    Had a chat today with another mechanic about diagnosing an overcharge. My question is - Is it possible to have a flashing sight glass if an overcharge exists?
    Yes it is.

    The total charge consists of high side charge plus low side charge.

    If too much of the charge is in the low side and not enough in the high side, the sight glass will have flashing.

    The sight glass only tells you about high side charge. It does not tell you about total charge.

    Oh... and if the valves in the compressor are blown out, the sight glass is not going to clear no matter how much refrigerant you stick in there.
    Last edited by Gary; 11-06-2009 at 05:50 AM.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: overcharge

    May I also add that a sight gas is absolutely useless as an charge indication.
    Unless the system is at full load!
    Then you may get a better indication of system charge.
    But as Gary has already explained they are not foolproof!
    Grizzly

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: overcharge

    If the expansion valve has failed in the fully open position, then the sight glass will be indicating bubbles or not be full as a result of the perceived demands of the system. You can easily grossly overcharge a system in these conditions and still not get a clear sight glass. The sight glass should only be used as an indicator. Full diagnosis of all measurable factors along with taking system pressures and temperatures should be reviewed before arriving at a conclusion.

  5. #5
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: overcharge

    Best possible diagnosis for overchatge will be high suction and high discharge,subject to your condensers are normal.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: overcharge

    The best indicators of overcharge (assuming good airflow through both coils) are:

    High subcooling (too much refrigerant in the high side)

    Low superheat (too much refrigerant in the low side)

  7. #7
    Join Date
    May 2009
    Location
    Canada
    Age
    41
    Posts
    6
    Rep Power
    0

    Re: overcharge

    If there is good air flow through both coils and the system is overcharged, yes you have high subcooling (too much liquid in the condenser) but how would you flash with all this subcooling? I have found many systems overcharged and corrected them but I have never seen flashing with an overcharge. Flashing with a dirty condenser yes but that is another topic.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: overcharge

    Quote Originally Posted by SL82 View Post
    If there is good air flow through both coils and the system is overcharged, yes you have high subcooling (too much liquid in the condenser) but how would you flash with all this subcooling? I have found many systems overcharged and corrected them but I have never seen flashing with an overcharge. Flashing with a dirty condenser yes but that is another topic.
    In the scenario outlined earlier by Hyperion, you could have flashing with overcharge. The subcooling would be low and the superheat would be low, the extra refrigerant being in the low side.
    Last edited by Gary; 12-06-2009 at 03:36 AM.

  9. #9
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: overcharge

    Quote Originally Posted by Gary View Post
    The best indicators of overcharge (assuming good airflow through both coils) are:

    High subcooling (too much refrigerant in the high side)

    Low superheat (too much refrigerant in the low side)
    Good points. Not so sure it's always perfectly cut-&-dried, though.

    To add to the debate, would an over-sized TX valve also not result in low superheat at evap exit?

    If so, how would you know whether the system was really overcharged, or as a consequence of the incorrect TXV selection?

    For instance, you can have a reasonable sub-cooling on the condenser, and low evap superheat. Would the system then be overcharged, or correctly charged?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: overcharge

    System problems need to be addressed in a particular sequence:

    First airflow problems.

    Then high subcooling problems.

    Then low superheat problems.

    Then wait until the refrigerated space is down close to design temp.

    Then high superheat problems.

    Then low subcooling problems.

    The correct question is not whether the system has an overcharge problem. The correct question is whether the system has a problem. And once we have resolved the problem, the next question is whether the system has another problem.
    Last edited by Gary; 12-06-2009 at 06:29 AM.

  11. #11
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: overcharge

    On more than one occassion I have come across jobs where oversized expansion valves have been fitted and the engineer has tried to charge the system to the sight glass and completely filled the receiver and condenser with so much liquid that there was no room to condense any more vapour which will result in the system cutting out on HP switch (if fitted) or the compressor stalling.

    A simple pump down test with your high side gauge on the discharge service valve of the compressor, pump down the system from the receiver service valve and observe the high side gauge as its pumping down, overcharge or non condensables in the system will soon get that high side gauge rising to the point of cutting off on HP switch.

    The above is based on a condensing unit with suction, discharge and receiver service valves fitted.

    I have also twice come across split air conditioners with sight glasses fitted in the expansion lines and massiveley overcharged to the point of the systems will not run, one was blowing off on the internal PRV of the compressor.

Similar Threads

  1. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  2. super heat and overcharge help for a noob
    By frostedflake in forum Trouble Shooting
    Replies: 11
    Last Post: 12-03-2009, 08:51 PM
  3. hot discharge air from C.U
    By ong in forum Fundamentals
    Replies: 48
    Last Post: 29-07-2005, 06:24 AM
  4. Refrigerant overcharge
    By frank in forum Air Conditioning
    Replies: 40
    Last Post: 09-03-2005, 11:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •