    no reciever no solenoid valve chilling system



    Not being a refrigeration engineer by the trade and the training, I need a bit of help from the professionals.

    What is the point of not using on such a chilling unit of neither receivers nor - what is more important - the liquid line solenoid valves:
    - two screw compressors (two separate R404a systems),
    - their air-to-air condensers are at roof,
    - their evaporators (beneath the compressors) are inside a common shell, chilling glycol ethylene water down to minus 8 C,
    - expansion devices are EEVs.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: no reciever no solenoid valve chilling system

    Not quite sure what your question is but...

    The EEV should be able to shut when no duty is required so a solenoid valve is not required.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: no reciever no solenoid valve chilling system

    The function of the line solenoid valve is prevention of liquid entering evap during compressor off times.
    They are a must, so far as I know, on the freezing systems. But I am unable to discern difference between some CHILLING systems equipped with sol valve and the others without.

  4. #4
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: no reciever no solenoid valve chilling system

    There are, nonetheless, EEV chillers both with solenoids and without - I forgot to add the last time.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: no reciever no solenoid valve chilling system

    an EEV can act as a SV.
    Why no receiver? Chiller manufacturers say you have to use the condenser at partial load. At partial load, you don't need that much condenser area, so you have spare condenser area to store and subcool liquid.
    All these machines are critical charged.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Oct 2007
    Location
    Not Sure?
    Posts
    76
    Rep Power
    17

    Re: no reciever no solenoid valve chilling system

    Chillers never shut off usually. They do not have a sol and receiver because they have bypass valves. This lets the system add refrigerant to the coil to maintain temp. They are critically charged and the hot gas valve and liquid injection valve is why this style is missing what you are use to.
    Seriously! What was that guy thinking.
    Pentane rocks!

Similar Threads

  1. Which chilling system?
    By chemi-cool in forum Commercial
    Replies: 5
    Last Post: 26-11-2008, 09:18 PM
  2. imi expansion valve problem
    By fridgemandan in forum Trouble Shooting
    Replies: 23
    Last Post: 08-10-2008, 08:48 PM
  3. R22 Flooded System - Trawler
    By chiefbecker in forum System Optimization
    Replies: 18
    Last Post: 08-02-2008, 12:11 AM
  4. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 04:42 PM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •