10-06-2009, 09:33 PM #1
no reciever no solenoid valve chilling system
Not being a refrigeration engineer by the trade and the training, I need a bit of help from the professionals.
What is the point of not using on such a chilling unit of neither receivers nor - what is more important - the liquid line solenoid valves:
- two screw compressors (two separate R404a systems),
- their air-to-air condensers are at roof,
- their evaporators (beneath the compressors) are inside a common shell, chilling glycol ethylene water down to minus 8 C,
- expansion devices are EEVs.
-
10-06-2009, 10:48 PM #2
Re: no reciever no solenoid valve chilling system
Not quite sure what your question is but...
The EEV should be able to shut when no duty is required so a solenoid valve is not required.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
11-06-2009, 07:18 AM #3
Re: no reciever no solenoid valve chilling system
The function of the line solenoid valve is prevention of liquid entering evap during compressor off times.
They are a must, so far as I know, on the freezing systems. But I am unable to discern difference between some CHILLING systems equipped with sol valve and the others without.
-
12-06-2009, 04:23 PM #4
Re: no reciever no solenoid valve chilling system
There are, nonetheless, EEV chillers both with solenoids and without - I forgot to add the last time.
-
13-06-2009, 07:31 AM #5
Re: no reciever no solenoid valve chilling system
an EEV can act as a SV.
Why no receiver? Chiller manufacturers say you have to use the condenser at partial load. At partial load, you don't need that much condenser area, so you have spare condenser area to store and subcool liquid.
All these machines are critical charged.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
15-06-2009, 03:21 PM #6
Re: no reciever no solenoid valve chilling system
Chillers never shut off usually. They do not have a sol and receiver because they have bypass valves. This lets the system add refrigerant to the coil to maintain temp. They are critically charged and the hot gas valve and liquid injection valve is why this style is missing what you are use to.
Seriously! What was that guy thinking.
Pentane rocks!
Similar Threads
-
Which chilling system?
By chemi-cool in forum CommercialReplies: 5Last Post: 26-11-2008, 09:18 PM -
imi expansion valve problem
By fridgemandan in forum Trouble ShootingReplies: 23Last Post: 08-10-2008, 08:48 PM -
R22 Flooded System - Trawler
By chiefbecker in forum System OptimizationReplies: 18Last Post: 08-02-2008, 12:11 AM -
Refrigeration system proposal; comments please.
By DaBit in forum Technical SpeculationsReplies: 13Last Post: 01-01-2003, 04:42 PM -
Automotive A/C Vent Temp Range vs System
By Don Browney in forum Air ConditioningReplies: 1Last Post: 15-05-2002, 06:19 AM