10-06-2009, 05:57 PM #1
small water chiller with blocked tubes
We have a small water chiller which has a shell and tube bundle. That water feeds a plate HE and in turn that water cools a machine.
The problem is we seem to have poor transfer from the S&T HE but good transfer from the Plate. So the shell water takes a real long time to recover and will rise even when cooling. It had a new compressor (two phasing on the contactor) and charge is weighed in.So we know the fridge side is good.
The ends of the S&T HE are welded on so we wonder how on earth would we be able to properly clean the thing. It's almost like a dirty hot water system which needs 'powerflushing'
Ideas?
10-06-2009, 07:31 PM #2
Re: small water chiller with blocked tubes
I don't think the problem is in the S&T.
You mention that the PHE works good, it only do so if the water feed is cool, on the other hand, where can dirt come in from?
Is it a closed system? Air vents?
I would give the refrigeration unit another check up.
10-06-2009, 08:15 PM #3
Hi Multisync
There are companies that chemical clean brazed Plate Heat exchangers and Shell and tube.
Perhaps someone can point you in the direction of one near you?
Do you have binder points across the s&t ?
10-06-2009, 08:40 PM #4
Is it a closed system? Air vents?on the other hand, where can dirt come in from?
10-06-2009, 09:36 PM #5
Given the water in and water out temps and the saturated condensing temp (SCT), we may be able to tell what the problem is.
11-06-2009, 01:06 PM #6
11-06-2009, 03:07 PM #7
Why not install a new S&T?
Looks like all the work around it will cost more.
Is this a Laser cutting machine?
York Chiller evap water flow direction
By mechillers in forum Technical DiscussionsReplies: 6Last Post: 30-03-2009, 05:37 PM -
water chiller question
By chillman in forum Technical SpeculationsReplies: 2Last Post: 12-03-2008, 09:21 PM -
Water Chiller
By lana in forum Technical SpeculationsReplies: 20Last Post: 23-06-2007, 01:19 AM -
Connecting Trane Water chiller to air handling unit
By celtictech in forum FundamentalsReplies: 10Last Post: 08-03-2007, 06:14 PM -