    Sealing Threaded joints with P.T.F.E.



    I was recently fitting some PRV,s (Changing single to dual style manifolds)
    and decided to use ptfe instead of loctite as it is more forgiving.
    Meaning the slightest movement when changing a prv and you have a leaking manifold. ( which is a gas out job!)
    Something in the back of my mind says that there are certain refrigerants that it's not recommended.
    To use ptfe does anyone know whether this is true?
    And if so which ones are a no no!
    Grizzly



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Sealing Threaded joints with P.T.F.E.

    I think its HFCs and the blends containing them, but thats only something i remember reading on here. I think some of the refrigerant bottles still use ptfe on the valves so maybe it is ok?

    I have been using that 'trublue' paste or whatever its called from rpw and not had any problems with i so far.

    So i'm not much help

    Jon

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Sealing Threaded joints with P.T.F.E.

    BOC are against using PTFE on any threads but in particular Oxygen because PTFE contains an oil based substance.
    Safe Under Pressure from BOC:- (might be handy for your gas storage question elsewhere Grizzly)

    https://b2.boc.com/gases/BOCInfo.nsf/webgenpres/F9D8B56CFB97F5A7802568A4005D6ACA/$file/SAFEUNDE.PDF

    (I had Firefox highlight this site because of a site certification problem but I accepted it and haven't had any problems.)

    Also, Safety Data Sheet for PTFE
    http://msds.chem.ox.ac.uk/PO/polytet...oethylene.html
    State - Incompatible with molten alkali metals, fluorine and other halogens, strong oxidizing agents.

    Last edited by Brian_UK; 09-06-2009 at 11:06 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Sealing Threaded joints with P.T.F.E.

    Grizz

    Don't use it on 404a, only loctite is acceptable, every joint we used to do leaked until we switched to loctite, eventually wholesalers got confirmation especially when fitting PRV's!! Not sure about 134a though, could be acceptable.

    al

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Sealing Threaded joints with P.T.F.E.

    I had some expensive experiences with PTFE tape and R22, great for a while then all started leaking.
    Went back to loctite. Currently using loctite 577, [ I think ] yellow looking stuff, on ammonia, good for sealing and does not go rock hard, easier to change when ever required .
    magoo

  6. #6
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Sealing Threaded joints with P.T.F.E.

    i used loctite 567 on everything,good for thread seal against moisture,after reading a bit more into data sheet i am now not so sure as it displays a thread tape property.thought i sussed it years ago.anyone got something that works everywhere.no leaks that i know of.spose we gotta solder in a tube bush then solder in ball valve tail,then pray that ball valve holds up,any laws about isolation valve before relief device
    mmm to beer or not to beer...........lets drink breakfast

  7. #7
    Join Date
    Mar 2009
    Location
    ireland
    Posts
    87
    Rep Power
    16

    Re: Sealing Threaded joints with P.T.F.E.

    i am with al on this copeland will only recommend loctite ... r404a will react with ptfe in time ..

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Sealing Threaded joints with P.T.F.E.

    Thank you my friends for the helpful advise.
    I will return the favour whenever I can!
    Well the afore mentioned job was on a 407c system.
    Time will tell as to if I have boobed or not.
    Let's hope not as it has over 80 KGS of refrigerant in it!!!
    Cheers Grizzly

  9. #9
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Sealing Threaded joints with P.T.F.E.

    IHello guys i thought the ester oil eats the ptfe tape

  10. #10
    Join Date
    Aug 2007
    Location
    Germany
    Posts
    36
    Rep Power
    0

    Re: Sealing Threaded joints with P.T.F.E.

    I would recommend Loctite 577 especially on larger bond gaps. It is important to use the original Loctite cleaner not any other solvent. You should take care not to pressurize the system to early, especially at low ambient temperatures.
    RTFM always thoroughly!
    Vacuum sucks!
    Sience rules!

  11. #11
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Sealing Threaded joints with P.T.F.E.

    i thought 577 was prone to moisture and have found when using on tx valve outlet it breaks down.
    mmm to beer or not to beer...........lets drink breakfast

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Sealing Threaded joints with P.T.F.E.

    Lowcool. The only type of valve before a safety relief is a double action valve with two safety valves, where one or the other is open to vessel at all times. This is covered in AS/NZS standards, for vessel design. And safety reliefs are to be tested and re-certified, or replaced every four years.
    magoo
    Last edited by Magoo; 13-06-2009 at 10:21 PM.

  13. #13
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Sealing Threaded joints with P.T.F.E.

    cheers magoo,thought their was something regarding this
    mmm to beer or not to beer...........lets drink breakfast

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Sealing Threaded joints with P.T.F.E.

    I use Leak Lock paste successfully on all refrigerants and oils. No leaks so far!
    http://www.highsidechem.com/lklcksp.html

    It is also part of Refco delivery program.
    Last edited by nike123; 14-06-2009 at 08:09 AM.

  15. #15
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: Sealing Threaded joints with P.T.F.E.

    Quote Originally Posted by nike123 View Post
    I use Leak Lock paste successfully on all refrigerants and oils. No leaks so far!
    http://www.highsidechem.com/lklcksp.html

    It is also part of Refco delivery program.
    Ive used this and seems ok its available from Javac in the UK

  16. #16
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Sealing Threaded joints with P.T.F.E.

    Hi Nike 123, thanks for referal to leak lock site.
    magoo

  17. #17
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Sealing Threaded joints with P.T.F.E.

    i used to use that stuff years ago,steered away from it because is it not user friendly.it hardens very well,is brittle and remains in threads,if someones been over zealous with the stuff before you and used it it in the wrong places its a female dog.if you want to do a quick tev change in a freezer to reduce ingress of moisture forget it.using to seal a removable fitting in a pressure vessel the stuff breaks apart and falls in,as is the usual case things dont fall out.think ill stick with loctite 567 and crank the hell out of the fitting.been doing it long enough now,as i said earlier i do not know of any leakage.
    mmm to beer or not to beer...........lets drink breakfast

  18. #18
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Sealing Threaded joints with P.T.F.E.

    Quote Originally Posted by Grizzly View Post
    Thank you my friends for the helpful advise.
    I will return the favour whenever I can!
    Well the afore mentioned job was on a 407c system.
    Time will tell as to if I have boobed or not.
    Let's hope not as it has over 80 KGS of refrigerant in it!!!
    Cheers Grizzly
    Hello Grizzly

    what about using lock tight along with the PTFE tape, the tape allows you to locate the PRV then the locktight sets and makes a permament seal.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  19. #19
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: Sealing Threaded joints with P.T.F.E.

    Andy, if you're using locktite and PTFE tape, you're still using PTFE tape.
    With all of the disadvantages exposed in this thread.
    So I'd say no.

    Does anyone still use litharge and glycerine?
    Or tin the thread with soft solder?
    I'm talking BSPT threads of course, not flares.
    For flares, I'd only use refrigeration oil.
    Last edited by Slatts; 19-06-2009 at 11:16 AM. Reason: more info.

  20. #20
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Sealing Threaded joints with P.T.F.E.

    ya gotta seal yea thread were da nut goes on da valve udderwise yon nut wood split from da ice.

    oh well
    mmm to beer or not to beer...........lets drink breakfast

  21. #21
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: Sealing Threaded joints with P.T.F.E.

    Quote Originally Posted by lowcool View Post
    ya gotta seal yea thread were da nut goes on da valve udderwise yon nut wood split from da ice.

    oh well
    Have you been giving those white cans a nudge lowcool?
    I can't understand your post.
    Are you one of those blokes who insist on putting thread tape on the thread of your flares?
    I've been doing this for over 30 years and never used thread tape on a flare on a TX valve and never had one crack.
    I did go through a phase a few years ago where I'd smear a film of Leaklock on the face of a flare, but I got over that.

    What was that awful beer that used to come out of your area? Southwark or some such name? I still shudder when I think of the QLD beer strike back in 1979.

  22. #22
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Sealing Threaded joints with P.T.F.E.

    Quote Originally Posted by Slatts View Post
    Have you been giving those white cans a nudge lowcool?
    I can't understand your post.
    Are you one of those blokes who insist on putting thread tape on the thread of your flares?
    I've been doing this for over 30 years and never used thread tape on a flare on a TX valve and never had one crack.
    I did go through a phase a few years ago where I'd smear a film of Leaklock on the face of a flare, but I got over that.

    What was that awful beer that used to come out of your area? Southwark or some such name? I still shudder when I think of the QLD beer strike back in 1979.
    gday slatts havent seen a white can around for a while,me nudge,heavens no i was just comparing the taste difference over 14 or 15 cans with irish whiskey and amaretto to keep the pallatte clean,woke up bit funny though less amaretto next time.definitely seal tx valve outlet "thread" everytime and would kick apprentice bum for not doing so,apart from ice splitting the nut there is also a tendency for the nut to loosen,southwark desperate times call for desperate measures,not a favourite of mine after travelling our wonderful country,can only suggest mixing it with coke.god should forbid beer strikes if he really loves us.
    mmm to beer or not to beer...........lets drink breakfast

  23. #23
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    64
    Posts
    113
    Rep Power
    16

    Re: Sealing Threaded joints with P.T.F.E.

    Each to their own low. I'm happy with a tape free thread on my valves. I do insist on the copper being soft when I flare it and if it's old, I anneal it first.
    The problems I've had with these flares are mostly due to valves being changed and the copper having hardened.
    If in doubt, cut it out, anneal it and re-flare it.


    When I lived in the Territory I moved between blue, green and white cans. Of course now my best drinking days are behind me and my kids remain mostly in ignorance of my past...

Similar Threads

  1. Vane compressor - axial sealing
    By gabim in forum Fundamentals
    Replies: 2
    Last Post: 08-04-2009, 07:45 PM
  2. Expansion Joints in the cold store floor
    By smpsmp45 in forum NH3
    Replies: 2
    Last Post: 17-05-2008, 07:47 AM
  3. Raised Distribution Joints
    By Husky250 in forum Air Conditioning