    Hi Guys anybody know anything about these units I have a system which Im trying to ID the Kw size
    the only info I have is:

    Indoor:40GKWX348W-703-40
    Outdoor :07KD036C9

    Ref: R22

    cHEERS IN ADVANCE



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Carrier water cooled split

    That size, 36, is 9.4kW cooling.

    Data table here
    http://eto.carrier.com/litterature/t...&lang_id=1.pdf

    If you want all the info on that model then start here...
    http://eto.carrier.com/lit.asp

    Click on 07KD in first box then select 'all types' in second box, press search.

    Do similar if you want the indoor unit stuff as well.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Carrier water cooled split

    Quote Originally Posted by flash View Post
    Hi Guys anybody know anything about these units I have a system which Im trying to ID the Kw size
    the only info I have is:

    Indoor:40GKWX348W-703-40
    Outdoor :07KD036C9

    Ref: R22

    cHEERS IN ADVANCE
    Carrier's nomenclature is based on 1,000's of Btu/hr. So the 07 (water cooled), KD model series, "036" is a nominal 36,000Btu/hr or 10.5kW. 9 or 913 or 903 at the end normally denotes a 3phase supply while 7 or 703 denotes 1 phase supply.
    Not sure if you've got the indoor unit number right. 40 series units are DX fan coils, GKWX could be OK, but 348 does not look right. O48 would be my guess (48,000BTU/hr). The 703 is 1 phase.

    Either way you are looking at a 9-10.5kW system.
    If in doubt read the instructions. If still in doubt follow them.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 12:25 PM
  3. water cooled subcooler?
    By star882 in forum Technical Speculations
    Replies: 1
    Last Post: 29-12-2007, 11:21 PM
  4. Making a simple water cooled condenser
    By The MG Pony in forum Fundamentals
    Replies: 19
    Last Post: 01-08-2007, 11:02 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •