    Question Help need - pressure test procedures



    Hi, all

    Old chap need your help ... there is a new European Standard EN378-2008, (standard which unfortunately, I do not have) ... with some ???? changes....


    Google was not of a big help ...but I believe to get more help here, as always


    I need to make a pressure test (strength and leak) on a big ammonia plant ...


    Regarding to maximum working pressure what are the pressure multiplication factors for strength and leak test pressure...


    Thanks for any help.

    Best regards, Josip



    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  2. #2
    kalaskar nares's Avatar
    kalaskar nares Guest

    Re: Help need - pressure test procedures

    I need calcullation capillary tube size and length. send to
    kalaskar_naresh@yahoo.com

  3. #3
    Join Date
    Apr 2009
    Location
    Durban
    Age
    70
    Posts
    31
    Rep Power
    0

    Re: Help need - pressure test procedures

    Google BS - EN 378-2 2008 Refrigerating Systems & Heat Pumps - you can purchase the standards off the relevant linked site.

    In South Africa we test to 1.1 times pressure vessel design pressure.

    Good Luck

  4. #4
    Join Date
    Mar 2001
    Location
    Derby, England
    Age
    58
    Posts
    86
    Rep Power
    24

    Re: Help need - pressure test procedures

    Stength test: 1.1 x maximum allowable pressure (MAP)
    Tightness test: 0.95 MAP

    Hope this helps

  5. #5
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Help need - pressure test procedures

    Hi Josip,
    Strength test = 1.3
    Pressure test = 1.1
    Air cooled condenser = 55 Degrees C
    Water cooled condenser = 43 Deg. C
    Low side of system = 32 Deg. C
    If you pm me your e-mail address I might have a bit more infromation for you.


    Cheers
    Tutto il Mondo e un Paese

Similar Threads

  1. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •