    Hi All,

    I have a 26 000btu General ceiling cassette heat pump type unit. The fuse on the outdoor unit keeps fusing. If I disconnect the compressor from the relay, it works fine, the relay switches without a problem. If I run the compressor on its own it also works fine. As soon as I connect the compressor up it will sometimes pop the fuse on start up. Any ideas?

    Help will be greatly appreciated.



  2. #2
    Join Date
    Feb 2007
    Location
    oldham
    Age
    49
    Posts
    44
    Rep Power
    0

    Re: General Cassette Fuse Problem

    breaker type and rating?

  3. #3
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: General Cassette Fuse Problem

    make sure that your cables resistance is ok as you may have either a faulty cable going to your contactor coil.
    also check the resistance of your contactor coil.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: General Cassette Fuse Problem

    What is model #?

  5. #5
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: General Cassette Fuse Problem

    I suggest the micro-relay's contacts on PCB are worn out - and at some times, when you are away, compressor's contactor, fed through that relay on PCB , begins frantically switching on and out. The fuse of the L to cassete blows out.

Similar Threads

  1. Fuji AOY45 cassette Problem (no heating)
    By R B M 72 in forum Air Conditioning
    Replies: 8
    Last Post: 09-03-2011, 08:30 PM
  2. Odd fuse blow
    By nike123 in forum Electrical
    Replies: 23
    Last Post: 12-01-2009, 09:34 AM
  3. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM
  4. Replies: 3
    Last Post: 04-03-2007, 07:03 PM
  5. LG 10.5 kw cassette timer problem
    By Andy W in forum Air Conditioning
    Replies: 10
    Last Post: 25-06-2005, 07:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •