General Cassette Fuse Problem
Hi All,
I have a 26 000btu General ceiling cassette heat pump type unit. The fuse on the outdoor unit keeps fusing. If I disconnect the compressor from the relay, it works fine, the relay switches without a problem. If I run the compressor on its own it also works fine. As soon as I connect the compressor up it will sometimes pop the fuse on start up. Any ideas?
Help will be greatly appreciated.
-
07-06-2009, 12:09 PM #2
Re: General Cassette Fuse Problem
breaker type and rating?
-
07-06-2009, 01:11 PM #3
Re: General Cassette Fuse Problem
make sure that your cables resistance is ok as you may have either a faulty cable going to your contactor coil.
also check the resistance of your contactor coil.
-
07-06-2009, 01:52 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: General Cassette Fuse Problem
What is model #?
-
07-06-2009, 03:40 PM #5
Re: General Cassette Fuse Problem
I suggest the micro-relay's contacts on PCB are worn out - and at some times, when you are away, compressor's contactor, fed through that relay on PCB , begins frantically switching on and out. The fuse of the L to cassete blows out.
Similar Threads
-
Fuji AOY45 cassette Problem (no heating)
By R B M 72 in forum Air ConditioningReplies: 8Last Post: 09-03-2011, 08:30 PM -
Odd fuse blow
By nike123 in forum ElectricalReplies: 23Last Post: 12-01-2009, 09:34 AM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM -
Problem with Mitsubishi Heavy Indusry Unit blowing 3 amp fuse
By kelvin01 in forum Air ConditioningReplies: 3Last Post: 04-03-2007, 07:03 PM -
LG 10.5 kw cassette timer problem
By Andy W in forum Air ConditioningReplies: 10Last Post: 25-06-2005, 07:09 PM