    Re: low high-side pressure, help



    Quote Originally Posted by mackking View Post
    no i didnt have a chance, but i would expect the pressure to rise since the refrigerant has nowhere to go, it would be compressed in the coil, hense the pressure should skyrocket.
    When you shut off the suction the compressor has nothing to pump into the high side... and the high side is still cooling off and draining off into the evaporator. If anything the high side pressure should drop.



  2. #102
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    the only other orifice i have is a .73, but when i installed it before it acted like it had too much restriction to flood the coil with enough refrigerant to keep it cool.
    Trust me, it will provide enough flow.

  3. #103
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    at this point i have nothin to loose so ill try the .73 again

  4. #104
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: low high-side pressure, help

    hi
    ithink there is miss matching btw the comp&air handler unit it appear that u have a large air hanling unit condenser came with this small orifice should b too small to handle the load u can check the comp brand & serial #

  5. #105
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by tonyelian View Post
    hi
    ithink there is miss matching btw the comp&air handler unit it appear that u have a large air hanling unit condenser came with this small orifice should b too small to handle the load u can check the comp brand & serial #
    I tend to agree about the mismatch. The evap seems oversized for the compressor, but then this could be simply an orifice mismatch.

    More worrisome is that the condenser seems oversized for the compressor.

    If the compressor is undersized (under-capacity) for both the evap and the cond, that probably means the compressor is inefficient.

    At this point I'm still hoping that the right sized orifice will show a good condenser load, but that may be just wishful thinking.

    As mackking says, at this point there is nothing to lose by trying another orifice.
    Last edited by Gary; 08-07-2009 at 09:41 PM.

  6. #106
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    i put in the .73, set it to 15f superheat but i still have a high pressure on the low side (85psi with a 66f suction line)
    the high side psi did rise but only to 225 psi. i couldnt get any more readings because it started pouring on me, but its still not bring the room temp down.

  7. #107
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    are u telling me that u think goodman installed the wrong compressor from the factory?

  8. #108
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    i put in the .73, set it to 15f superheat but i still have a high pressure on the low side (85psi with a 66f suction line)
    the high side psi did rise but only to 225 psi. i couldnt get any more readings because it started pouring on me, but its still not bring the room temp down.
    Any idea what the indoor and outdoor temps were at the time you took those readings?

  9. #109
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    are u telling me that u think goodman installed the wrong compressor from the factory?
    No... an inefficient compressor is one with broken valves. The symptoms are the same as having an undersized compressor.

  10. #110
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    yeah the air in evap was 79 and the air out was 62, i know there is a good difference but it still dont seem cold enough to me.

  11. #111
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    how would i confirm an inefficient compressor

  12. #112
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    yeah the air in evap was 79 and the air out was 62, i know there is a good difference but it still dont seem cold enough to me.
    And what was the outdoor temp?

  13. #113
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    i couldnt check it at the time because of the rain but i thinkit was around 85

  14. #114
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    As the temp in the house comes down the superheat will drop, so you should remove some refrigerant to keep it up around 15F.

  15. #115
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    i couldnt check it at the time because of the rain but i thinkit was around 85
    225 psi at 85F would be an improvement. There may be hope for this system yet.

  16. #116
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    there may be hope but it hasnt brought it down and shut off yet, do u think this is any indication of how its gonna perform?

  17. #117
    Join Date
    Mar 2007
    Location
    USA
    Posts
    118
    Rep Power
    18

    Re: low high-side pressure, help

    I have to wonder if pix would help. There may be a surprise in store. It has happened with other threads.

  18. #118
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    what kind of pics do u want?

  19. #119
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    there may be hope but it hasnt brought it down and shut off yet, do u think this is any indication of how its gonna perform?
    To get the charge just right, you need to adjust to 15F superheat when the house is down to your shutoff temp. We've been just ballparking it to compare orifices.

  20. #120
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    is the superheat effected by night time or daytime?

  21. #121
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    it just shut off!!

  22. #122
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    from 830 to 12 to drop it 8f

  23. #123
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    When it comes back on would be the best time to adjust the charge.

  24. #124
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    will the superheat skyrocket during the heat of the day? or should it stay pretty much the same?

  25. #125
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    will the superheat skyrocket during the heat of the day? or should it stay pretty much the same?
    The superheat will be higher when the house is warm.

  26. #126
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    from 830 to 12 to drop it 8f
    You are not only cooling the air in your house... you are cooling everything in your house. And you are also dehumidifying everything. It has been very humid lately.

  27. #127
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    yeah i know

  28. #128
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    so far its holding 70f in the room, but it has been overcast and raining today too. so far so good

  29. #129
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Got a full list of temps/pressures?

  30. #130
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    nope still rainin, but its running about 35-45 minutes during cycles

  31. #131
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Did you trim the charge to 15F superheat?

  32. #132
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    i got in contact with goodman tesh support, they said the system required a .73 orifice(which i installed) and a superheat of 22f because uf the humidity. i did this yesterday and it has worked the best today but like i said it was overcast and raining. anyways here are the reading-
    suction temp=62f
    liquid line=83f
    condensor in=77f
    condensor out=88
    evap in=66
    evap out=53
    lowside=72psi
    highside=175psi

  33. #133
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    this was taken at 10pm and it was wet, 95% relative humidity

  34. #134
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Low delta-T's... high suction... low head... I'm thinking this compressor is inefficient.

    The only other possibility would be a leaking reversing valve, but you checked the suction pressure on both sides of the reversing valve and they were identical.

  35. #135
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    I found a Goodman service manual:

    http://www.hvacpartsshop.com/asc%20series.pdf

  36. #136
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: low high-side pressure, help

    hi
    ur air handler is 3.5 tons&condenser is 3 tons there is a miss match
    gary tanks for the link&the way u guide him
    i think every thing is clear now

  37. #137
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    The air handler is rated at 2.5 to 3.5 tons, based on 400CFM per ton. It is currently set on low speed (1000CFM) which should result in a low suction pressure... but the suction pressure is in fact high.

    One more thing we can try is to measure the temps of the two cold pipes at the reversing valve. If the valve is leaking across, the temp on the side towards the compressor will be considerably higher.

  38. #138
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    would a leaking reversing valve of an inefficient conpressor still pull a vacuum when the suction line is closed?

  39. #139
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    you asked if it would pull a vacuum, it did but it didnt do it fast and it wasnt much. ive seen systems with a clogged orifice and they would pull a hard hacuum very quickly.

  40. #140
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    also as a bit of info, the tech at goodman said he didnt think the highside pressure was low. but as im learning more of how the system works, it seems it would need a higher pressure to keep the refriderant from boiling in the liquid line, right?

  41. #141
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Where are you measuring the evap air in and air out temps? Best would be at the air handler.

  42. #142
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    the return air is right above the air handler about 1ft and the closest out is at a vent 3ft away. its a downdraft.

  43. #143
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    i cant measure the out temp right from air handler because it mounts to the floor so i have to use the closest vent

  44. #144
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    3 ft away should be accurate.

  45. #145
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    it seems it would need a higher pressure to keep the refriderant from boiling in the liquid line, right?
    Uhhh... No.
    Last edited by Gary; 11-07-2009 at 04:59 AM.

  46. #146
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    also as a bit of info, the tech at goodman said he didnt think the highside pressure was low.
    I would disagree. Generally the SCT is 20-35F above the temp of the air entering the condenser (20-35F TD), depending upon load and relative coil size. I have yet to see the TD hit 20F despite the high suction pressure.
    Last edited by Gary; 11-07-2009 at 05:06 AM.

  47. #147
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    Quote Originally Posted by Gary View Post
    Uhhh... No.
    in reading your post in a/c 101, you explained that the boilding of refrigerant in the evaporator removes the heat from the air(which i understand) but i also understood it to say by raising the pressure in the condensing coil it returned the refrigerant back to a liquid(by increasing pressure and removing the added heat) so i guess my question is, is the system raising the pressure enough to maintain the proper liquid state?

  48. #148
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    my next question is, by overcharging and having the wrong orifice, could that have damaged the valves in the compressor?

  49. #149
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    in reading your post in a/c 101, you explained that the boilding of refrigerant in the evaporator removes the heat from the air(which i understand) but i also understood it to say by raising the pressure in the condensing coil it returned the refrigerant back to a liquid(by increasing pressure and removing the added heat) so i guess my question is, is the system raising the pressure enough to maintain the proper liquid state?
    R22 at 175psi gives you a saturated condensing temp (SCT) of 93F. In order for the liquid in the liquid line to boil off, its temp would have to be higher than 93F. Its temp is 83F. Not going to happen... and since the two temps go up and down together, it can't happen.
    Last edited by Gary; 11-07-2009 at 04:54 PM.

  50. #150
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    my next question is, by overcharging and having the wrong orifice, could that have damaged the valves in the compressor?
    Yes... it could.

Page 3 of 4 FirstFirst 1234 LastLast

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  4. High Pressure Freezing
    By mattynige in forum New Technologies
    Replies: 9
    Last Post: 19-06-2008, 02:03 PM
  5. discharge pressure too high
    By zahar in forum Trouble Shooting
    Replies: 7
    Last Post: 16-02-2008, 08:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •