    Re: low high-side pressure, help



    there is no other high side tap



  2. #52
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    there is no other tap in the high side

  3. #53
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Ok... then we have no choice but to trust the high side pressure measurement at the shutoff tap.

  4. #54
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    ok the stat says 76 room temp
    evap-air in 76
    air out 65
    condensor- air in 79
    air out 88
    suction line temp 72
    liquid line 89
    low side pressure= 66 psi
    high side pressure=170 psi
    suction line temp is 72F
    saturated suction temp for R22 @ 66 psi is 38F

    72 - 38 = 34F superheat

    Add refrigerant slowly until the superheat is about 15F, then take a new full set of temp and pressure readings.

  5. #55
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: low high-side pressure, help

    hi
    is the unit is enough for the area coverd more detail pls
    size of both orifices &u fitted with o ring&right direction
    did condensing unit match air handling
    more detail pls

  6. #56
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    suction line= 56f
    liquid line=93f
    low side=85psi
    high side=200psi
    condensor air in=82f
    condensor air out=94
    evap air in=77f
    evap air out=59f

  7. #57
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    its a 3 ton goodman heat pump with matching air handler (both brand new).
    its in a 900sq ft mobile home (with a lot if insulation).
    the indoor orfice is a .82 and the outdoor orfice is a .55
    both are in correctly and workin correctly

  8. #58
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    The .082 orifice is too large and is overloading the system. You need to switch to the .078 and then take a new set of readings.
    Last edited by Gary; 06-07-2009 at 03:58 AM.

  9. #59
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    i know the orfice is too large but when i put the .78 in, the vent temp rose 8f

  10. #60
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    We need to get everything in balance. And at this point the orifice is too large.

  11. #61
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    ok ill put it back in but how will i get the temp down
    how cold can i make it get?

  12. #62
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    am i expecting too much from this unit? because i really expected to see temps in the 40's.

  13. #63
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    it would seem that my understanding of how the system works is wrong, so what directly determinds how cold the coil gets?

  14. #64
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Planning on turning your mobile home into a refrigerator?

  15. #65
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Once we get the system in balance the next step will be to reduce the blower speed.

  16. #66
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    well kinda, i just want it to cycle during the day instead of running all the time. i keep the stat set on 70f, during the day it get up to about 82 of 83. when night falls, it takes it until 2am to bring it back down to 70.
    i would have said that it was an insulation problem, but i rebuilt the house last year and completely packed every wall with styrofoam and fiberglass insulation then sealed the outside with thermoply before putting the siding back on. also if it were an insulation problem, i would figure it would recover fast at night or during the rain but it dont. and im trying to reduce my light bill from $400.

  17. #67
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    well kinda, i just want it to cycle during the day instead of running all the time. i keep the stat set on 70f, during the day it get up to about 82 of 83. when night falls, it takes it until 2am to bring it back down to 70.
    i would have said that it was an insulation problem, but i rebuilt the house last year and completely packed every wall with styrofoam and fiberglass insulation then sealed the outside with thermoply before putting the siding back on. also if it were an insulation problem, i would figure it would recover fast at night or during the rain but it dont. and im trying to reduce my light bill from $400.
    I have 3 tons for 1500 sq ft and it pulls down pretty fast. For 900 sq ft it should pull down very fast... but first we need to get it working right.

  18. #68
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    i couldnt agree more. ive never had this much trouble. ive always just charged a system to 72psi on the low side and it worked but like i said i havent done a whole lot of it.

  19. #69
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    i couldnt agree more. ive never had this much trouble. ive always just charged a system to 72psi on the low side and it worked but like i said i havent done a whole lot of it.
    I've heard of a lot of different ways to charge a system, but that is probably the worst.

  20. #70
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    BTW, right now you have 6F superheat, which means the system is overcharged. I clearly remember saying charge it to 15F superheat.

  21. #71
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    well maybe before this is all said and done, ill know the correct way. its sure been a learning experiance.

  22. #72
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    You might want to read through this thread:

    http://www.refrigeration-engineer.co...ad.php?t=19701

  23. #73
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: low high-side pressure, help

    hi
    ur orifice size should be 065 indoor&o70 outside

  24. #74
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    ok i put the .78 back in and reset it and set the evap blower to low(from medium)
    suction line=62f
    liquid line=88f
    lowside=80psi
    highside=190psi
    condensor in=79f
    condensor out=89f
    evap in=76f
    evap out=60f

  25. #75
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    the .78 came with the air handler and the .58 was factory installed in the condensor. from all the experiments ive tried, when i install a smaller orifice, the vent temp rises. my only explination is that when i install a smaller orifice, it restricts the refrigerant flow too much and cant keep up with the coil. but i could be wrong.

  26. #76
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    With suction pressure that high the discharge pressure should be much higher. I'm thinking you may have an inefficient compressor.

    Close the suction line shutoff valve and see if the compressor will pump down into a vacuum.

  27. #77
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    what would cause the compressor to be inefficient? and what would cause two of them to be? like i said before, this is the second system and both of them act the exact same way. i have examined both refrigerant lines inside and out and both are fine and restriction free.

  28. #78
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    um not very well. it pulled it to a 8inhg vacuum. is that enough? or could it be the reversing valve leaking? i have questioned the reversing valve all along but i dont know how to check it.
    it doesnt seem to have much efficientcy in heat mode either but that could be a compressor too, right?

  29. #79
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    I found a piston kit chart. Let's see if we can find the official right size:

    http://site.famousparts.com/goodman/PDF/PKC-00U.pdf

  30. #80
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    the condensor is a model # gsh130361bb
    the air handler is a model#
    adpf304216ba
    i couldnt find the exact app for this unit in the charts.

  31. #81
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    oh i dont know if it matters, but whan i closed the suction shut-off valve, the high side pressure DID NOT rise.

  32. #82
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Is there a model# on the coil?

  33. #83
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    oh i dont know if it matters, but whan i closed the suction shut-off valve, the high side pressure DID NOT rise.
    Did the low side pressure at the compressor inlet go into a vacuum?

  34. #84
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    which coil? but probly not there is not alot of id numbers on it

  35. #85
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    not much of a vacuum, 8 inhg

  36. #86
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    which coil? but probly not there is not alot of id numbers on it
    The indoor coil.

  37. #87
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    the condensor is a model # gsh130361bb
    the air handler is a model#
    adpf304216ba
    i couldnt find the exact app for this unit in the charts.
    The ADPF304216BA can have a 2.5 to 3.5 ton coil.

    As near as I can tell a 2.5 ton needs .065 and a 3.5 ton needs .078

  38. #88
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    i cant find any other numbers, so what do u think about the vacuum and pressure?

  39. #89
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    i was told that the air handler was built to range from a 2 1/2 ton -3 1/2 ton, making it a good candiate for my 3 ton condensor

  40. #90
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    I am not ready to blame the compressor just yet. We need to get the right orifice in there and see what the temps/pressures tell us.

    The .078 is just too large, so we can assume that the coil is not 3 1/2 ton.

    Unless you can find the btu rating for the coil we will just have to keep changing orifices.

    I want to see that suction pressure down around 70 psi (or a little less) with about 15F coil outlet superheat.
    Last edited by Gary; 07-07-2009 at 05:47 PM.

  41. #91
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    well before i knew about the superheat method, i was setting the suction pressure at 70psi or little below, and when i put in smaller orifices(trying to raise the head pressure) i would loose a significant amont of efientcy. wich is how i ended up with the .82 orfice, the gave me the coldest vent temp.
    it still really concerns me, that when i shut off the suction valve completly, the high side didnt change but the low side came down to a small vacuum. before i blamed the compressor, i would question the reversing valve, but i dont know how to check it.

  42. #92
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    You keerp mentioning the vent temp as if it were important.

  43. #93
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    if it dont blow cold then whats the point?

  44. #94
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    60f just isnt cold

  45. #95
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    if it dont blow cold then whats the point?
    The point is transferring heat.

  46. #96
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    call it whatever you like but the whole fact of the matter is that it cant transfer heat if it cant make heat, and with a head pressure of 180psi, it cant make heat. and when i close off the suction line and it still dont raise the head pressure, nothing will no matter how many orifices i throw at it.

  47. #97
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Quote Originally Posted by mackking View Post
    call it whatever you like but the whole fact of the matter is that it cant transfer heat if it cant make heat, and with a head pressure of 180psi, it cant make heat. and when i close off the suction line and it still dont raise the head pressure, nothing will no matter how many orifices i throw at it.
    Why would you expect the head pressure to rise when you shut off the suction valve?

  48. #98
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: low high-side pressure, help

    Did you try another orifice today?

  49. #99
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    no i didnt have a chance, but i would expect the pressure to rise since the refrigerant has nowhere to go, it would be compressed in the coil, hense the pressure should skyrocket.

  50. #100
    Join Date
    Jun 2009
    Location
    florida
    Posts
    77
    Rep Power
    15

    Re: low high-side pressure, help

    the only other orifice i have is a .73, but when i installed it before it acted like it had too much restriction to flood the coil with enough refrigerant to keep it cool.

Page 2 of 4 FirstFirst 1234 LastLast

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  4. High Pressure Freezing
    By mattynige in forum New Technologies
    Replies: 9
    Last Post: 19-06-2008, 02:03 PM
  5. discharge pressure too high
    By zahar in forum Trouble Shooting
    Replies: 7
    Last Post: 16-02-2008, 08:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •