04-07-2009, 07:32 PM #11
Re: low high-side pressure, help
High temp liquid exits the metering device and then flashes off to reduce its temp to saturation. The temp in between can be anywhere in between. The correct temp at this point is "whatever it needs to be". So... measuring the flash temp tells you absolutely nothing useful.