Page 4 of 4 FirstFirst 1234
Results 151 to 166 of 166
  1. #151
    Apr 2001
    79
    5,071
    35
    Re: low high-side pressure, help
    Did you measure the temps of the suction lines entering and leaving the reversing valve?
  2. #152
    Jul 2006
    usa
    it sounds like you are closer to getting it. if not what I would do is recovery the refrigerant, return both units to goodman specs, evacuate according to goodman instructions. Then weigh in the factory charge and weigh the additional charge according to what Goodman says - for example .68 oz or each additional foot beyond 15 feet. I have seen it stated to recovery refrigerant for less then 15 feet also.
    If this does not give you a good operating ac then call goodman and say what the ....
  3. #153
    Jul 2006
    usa
    The other thing is where is the expansion valve? I do not have much experience with Goodman but it seems all manufactures have gone with txvs since the high SEER. Could you have a 13SEER Cond and a 10SEER Evap coil?
    A txv might work better anyhow
  4. #154
    Jun 2009
    florida
    77
    the epansion orifice is in the front of the case. i am pretty sure its a 13seer handler too. and as far as it having a txv, the handler i removed had a txv and i didnt like it. i would prefer to have an orifice simply because its just less to question its functionality.
  5. #155
    Jul 2006
    usa
    to me a txv is much easier. I've always had good luck with weighing in a charge - estimating distance if I did not install the lineset. Check subcooling and everything works out.
    Since the txv meters the refrigerant by suction temp I'd think you get better performance.
    As for fouling the txv it is just as likely to plug the orifice with a dirty lineset.
  6. #156
    Jun 2009
    florida
    77
    this is true. everyone prefers different things, ive just had better luck with orifices.
  7. #157
    Jun 2009
    florida
    77
    i cant see a difference in the temps on the reversing valve. also, when i would pump the system into the condensor to change the orifice, it would hold the pressure in the highside and not bleed back to the lowside, so i think the valve is fine. as for the compressor, im not sure.
  8. #158
    Apr 2001
    79
    5,071
    35
    Yep... everything points to the compressor.
  9. #159
    Jun 2009
    florida
    77
    is it likely to have 2 compressors, from 2 separate units, built by different companies, be inefficient? i guess thats my doubt.
  10. #160
    Jun 2009
    florida
    77
    one being used but worked when removed other than a leak in the condensing coil(which i fixed) and the other being brand new.
  11. #161
    Apr 2001
    79
    5,071
    35
    I have no way of knowing what the other unit did or did not do.
  12. #162
    Jun 2009
    florida
    77
    it had the exact pressure characterisitcis, but it was older and i didnt know much about it, other than it ran but had a leak. it did however have a lower head pressure and a higher suction pressure then normal. like the one i have now.
  13. #163
    Apr 2001
    79
    5,071
    35
    What are the make and model number for your compressor?
  14. #164
    Jun 2009
    florida
    77
    ill have to take it apart to get them, but it is a recipricating compressor.
  15. #165
    Jun 2009
    florida
    77
    i dont know if i told u, but i really appeciate all your help and advice. you have taught me alot in the last week or so
  16. #166
    Apr 2001
    79
    5,071
    35
    Glad to help.
  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Last Post: 19-07-2011, 03:16 AM
  2. High discharge temp
    By paul_h in forum Air Conditioning
    Last Post: 06-05-2009, 11:10 AM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Last Post: 10-03-2009, 01:03 PM
  4. High Pressure Freezing
    By mattynige in forum New Technologies
    Last Post: 19-06-2008, 02:03 PM
  5. discharge pressure too high
    By zahar in forum Trouble Shooting
    Last Post: 16-02-2008, 08:58 PM