Re: Optimization of the refrigeration plants operation
When the weather change operating of evaporative condensers will change.Optimum set point should be readjusted. For example. Optimum wet bulb approach is 10degF. During the day wet bulb temp. is 75 degF so optimum head pressure will be 75+10=85degF or 150psig. During the night wet bulb drop to 60F and optimum head pressure will be 60+10=70F or 115psig. Capacity of evaporative condensers should be readjusted.