05-06-2009, 05:53 AM #1
dakin split
hi ,its my first time on here ,,,just wondered if any 1 can help. ive gat a daikin 407 split system ..its not running ,, its got an e4 fault code on the display .. which i know is a low pressure problem ,, have reclaim the gas and leaked tested , no problems found ,, so i recharged the system .. still didnt run,, when i pushed the contacter 2 get the compressor 2 run the suction and the high side both went down 2 -1 on the gauges .. just like it was vacing it self down ..changed the pc board but still doing the same thing ..has any 1 got any ideas
many thanks
rich
-
05-06-2009, 09:29 AM #2
Re: dakin split
hi there richard , where do you have your guages connected ? are they both on the suction side? . are all valves open to the indoor unit?
-
05-06-2009, 02:35 PM #3
Re: dakin split
hi ya ,,the gauges are on the suction and the discharge ..i have checked 2 make sure the valves r open on the unit ..i thought some 1 had shut the discharge side myself ... cos it seems like the unit is pumping it self down
any help would be greatfull
thanks rich
-
05-06-2009, 02:53 PM #4
Re: dakin split
Hi Rich, did you check the low pressure sensor?
-
05-06-2009, 04:28 PM #5
Re: dakin split
Are the indoor fans running? What are the air on/air off temps?
-
05-06-2009, 05:41 PM #6
Re: dakin split
is your wriring correct connected??
Ice
-
05-06-2009, 07:17 PM #7
Re: dakin split
what is the expansion device?if cappilary then sounds like the strainer is blocked or some where in expansion line!how much refirgerant did you reclaim?
-
15-06-2009, 10:28 PM #8
Re: dakin split
had problems with 407 daikin before was suction strainer colapsed inside and blocked caused by liquid slugging symptoms are unit appears to pump down was 10 kw wall
-
16-06-2009, 12:18 AM #9
Re: dakin split
Rich,
Is one of your gauge lines connected inside the outdoor unit or are they both on the outside of it?
Is it a heat pump or cooling only?
Assuming both your hoses are connected on the outside of the outdoor unit, it is likely that you are looking at a blocked strainer/ cap tube or a failed EEV (most likely the EEV's motor or actuator, have you checked the lead between that and the PCB?)
Happy hunting.
If you got a model no, I will dig out the wiring diagram.
Similar Threads
-
3 single split units or one multi split - consumer advice needed
By kok in forum Air ConditioningReplies: 18Last Post: 15-04-2009, 08:42 PM -
Sensible Heat Factor / capacity of Inverter split Systems at part load?
By Greengrocer in forum Technical SpeculationsReplies: 31Last Post: 09-02-2009, 04:57 PM -
Anyone know of a decent brand 6kw wall split with 1/4 x 5/8 lines?
By paul_h in forum Air ConditioningReplies: 21Last Post: 12-11-2008, 05:43 PM -
Australian split installers, some info needed
By paul_h in forum Air ConditioningReplies: 10Last Post: 20-05-2008, 03:40 PM -
Do you beleive in data of split units?
By jirhol in forum FundamentalsReplies: 4Last Post: 29-03-2008, 11:17 PM