    dakin split



    hi ,its my first time on here ,,,just wondered if any 1 can help. ive gat a daikin 407 split system ..its not running ,, its got an e4 fault code on the display .. which i know is a low pressure problem ,, have reclaim the gas and leaked tested , no problems found ,, so i recharged the system .. still didnt run,, when i pushed the contacter 2 get the compressor 2 run the suction and the high side both went down 2 -1 on the gauges .. just like it was vacing it self down ..changed the pc board but still doing the same thing ..has any 1 got any ideas

    many thanks

    rich



  2. #2
    Join Date
    Jan 2008
    Location
    New Zealand
    Age
    50
    Posts
    27
    Rep Power
    0

    Re: dakin split

    hi there richard , where do you have your guages connected ? are they both on the suction side? . are all valves open to the indoor unit?

  3. #3
    richardrichard's Avatar
    richardrichard Guest

    Re: dakin split

    hi ya ,,the gauges are on the suction and the discharge ..i have checked 2 make sure the valves r open on the unit ..i thought some 1 had shut the discharge side myself ... cos it seems like the unit is pumping it self down
    any help would be greatfull
    thanks rich

  4. #4
    Join Date
    May 2009
    Location
    Querétaro México
    Age
    62
    Posts
    24
    Rep Power
    0

    Re: dakin split

    Hi Rich, did you check the low pressure sensor?

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: dakin split

    Are the indoor fans running? What are the air on/air off temps?

  6. #6
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: dakin split

    is your wriring correct connected??

    Ice

  7. #7
    Join Date
    May 2008
    Location
    poole
    Age
    38
    Posts
    17
    Rep Power
    0

    Re: dakin split

    what is the expansion device?if cappilary then sounds like the strainer is blocked or some where in expansion line!how much refirgerant did you reclaim?

  8. #8
    Join Date
    May 2009
    Location
    uk
    Age
    62
    Posts
    44
    Rep Power
    0

    Re: dakin split

    had problems with 407 daikin before was suction strainer colapsed inside and blocked caused by liquid slugging symptoms are unit appears to pump down was 10 kw wall

  9. #9
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: dakin split

    Rich,

    Is one of your gauge lines connected inside the outdoor unit or are they both on the outside of it?
    Is it a heat pump or cooling only?

    Assuming both your hoses are connected on the outside of the outdoor unit, it is likely that you are looking at a blocked strainer/ cap tube or a failed EEV (most likely the EEV's motor or actuator, have you checked the lead between that and the PCB?)

    Happy hunting.


    If you got a model no, I will dig out the wiring diagram.

Similar Threads

  1. Replies: 18
    Last Post: 15-04-2009, 08:42 PM
  2. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM
  3. Replies: 21
    Last Post: 12-11-2008, 05:43 PM
  4. Australian split installers, some info needed
    By paul_h in forum Air Conditioning
    Replies: 10
    Last Post: 20-05-2008, 03:40 PM
  5. Do you beleive in data of split units?
    By jirhol in forum Fundamentals
    Replies: 4
    Last Post: 29-03-2008, 11:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •