Results 1 to 6 of 6
Thread: error 01 on sanyo unit
-
04-06-2009, 09:29 PM #1
error 01 on sanyo unit
Hi ,its my first post and i need some help. I have problem with 4 air conditioner which ocur at same time when electican was fixing something . They all start blinking this error 01 and nobody here(Croatia) is not able to fix that problem. I know is some comunication problem beetwen units but nobody is able to fix.
Can some explain to me what i should do ????
Thanks and regards from Croatia
-
04-06-2009, 10:40 PM #2
Re: error 01 on sanyo unit
Zoran
check out the link below.
And yes it is a communication problem!
Grizzly
http://www.mediafire.com/?d0eyzznyyol
-
04-06-2009, 10:58 PM #3
Re: error 01 on sanyo unit
Hi Zoran.
check out the attached
It is what I think you need?
Grizzly
-
29-06-2009, 01:35 PM #4
Re: error 01 on sanyo unit
E01 is as follows
Error in receiving a signal from main indoor unit in group control.
Check the following
Outdoor unit address set not complete. Re address the system to be sure..
Individual sub / main address settings are not set for group control.
First check wiring for group setting NB> all indoor units in a group(connected to one remote) are wired together on their remote control terminals.
Then if you can access the detailled setting data.
Press buttons spanner/set and clr for 4 seconds the display will change. and code 11 will appear on right hand side of controller .
Use the temp up button to advance to code 14.
Check the setting of this It is displayed above the clock arrows. EG 99 or 0001 or 0002 .
use the unit button to scroll between the differant indoor units connected to the remote controller to check this code setting on differant indoor units
This has to be set as follows
The master unit in the group can be set to 0001
all other units in a group set to 0002.
To change this setting use clock up and down buttons and press set button to register a change.
If this does not sort your problems drop me a line
and we can try again.
One important thing only 8 indoor units can be connected as a group.
Regards
T
-
29-06-2009, 09:38 PM #5
Re: error 01 on sanyo unit
On the outdoor unit circuit board there is an auto address button, if the units have been turned off by the electrician while he was working this can cause a fault on some of the units i have installed.
Press the auto address button till you see two (maybe green) lights blinking and it will find its indoor unit, this has worked for me on Sanyo equipment after a power failure etcLast edited by Brian_UK; 10-07-2009 at 10:34 PM. Reason: Removed word processor data.
-
10-07-2009, 10:12 PM #6
Re: error 01 on sanyo unit
Please remember to include the model # and serial number.
Sanyo's website is sanyohvac/com and has the manuals on line.
hope this helps in the future
Koldman
edit: Sanyo website = http://www.sanyohvac.com/Last edited by Brian_UK; 10-07-2009 at 10:37 PM. Reason: Added Sanyo url - good link, thanks, Brian
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
fault on a sanyo unit
By marc5180 in forum Air ConditioningReplies: 7Last Post: 18-08-2007, 11:04 PM -
Sanyo inverter split unit
By cikku in forum DomesticReplies: 3Last Post: 22-05-2006, 06:07 PM