Results 1 to 17 of 17
Thread: Promac portable air conditioners
04-06-2009, 02:04 PM #1
Hey guys, calling to all you experts out there!! We have a portable Promac, model number : PM29CM, serial: 2001420, the unit works ok but the only drawback is that the compressor is running freaking hot
( compressor RECHI number: 44R261A
serial: RL22GC0151) I've put a thermometer on it and it reads 140 degrees fahrenheit . It had some rubbers things on the high side tubing and it melted But the supply temperature is fine 46 degrees F, the amps is 8.2 and the pressures are fine.
What's the acceptable working temperatures on the compressor body.
I know that it worked a long time with a dirty condenser, we cleaned it good but stills run hot. I work in an hospital and we have a few of them ( about 50 )
and it's the second time this happens.
Can't wait to read your quality answers.
04-06-2009, 03:16 PM #2
Re: Promac portable air conditioners
If it is a rotary compressor the body is part of the high side and should be hot.
(You can tell its a rotary compressor if it has an accumulator welded on the side of it)Last edited by Gary; 04-06-2009 at 03:20 PM.
04-06-2009, 04:08 PM #3
It is a rotary compressor, but it's the first time, well actually the second, that I come across a compressor THAT hot, like I said, there are some anti-vibration rubber things that are glued on the lines and they literally melted, I've had rotary compressors on window units and that problem never happened...and don't you find that 140 degrees F is way too hot ??
Thanks for your quick answer friend
04-06-2009, 05:44 PM #4
04-06-2009, 05:47 PM #5
heres the thread
http://newsgroup.derkeiler.com/Archi.../msg00526.html
it's in french but you surely can translate it.
04-06-2009, 06:26 PM #6
I would reduce the load on the poor thing (the comp.) - by reducing air flow through evap. Maybe it (comp.) then gets some less superheated gas and becomes less hot.
04-06-2009, 06:57 PM #7
04-06-2009, 07:00 PM #8
04-06-2009, 07:00 PM #9
What is the compressor inlet superheat?
05-06-2009, 12:12 PM #10
I do too Gary find it hard to believe, I will run some tests on other rotary compressors, I think that the problem could be that the compressor is not ventilated like window units...in these portable air conditioners the compressor is not ventilated and is in a closed space. By the way Gary, could you please tell me specifically how does an accumulator works and it's purpose, we've been having discussions about it at work and if I win my bet, I'll e-mail you your share, HA HA!! I thank you a zillion times Gary for you quick and quality answers.
05-06-2009, 12:26 PM #11
Check the link...but I'm not sure the compressor is the cause...
http://www.youtube.com/watch?v=OqHwVAiI-ZQ
05-06-2009, 04:04 PM #12
If you look closely, the electrical terminals shorted out on the top of the compressor.
05-06-2009, 07:21 PM #13
05-06-2009, 08:50 PM #14
I never saw an AC's comp ventilated, on the contrary, they are "clothed and buttoned".
On my view, portables should be better chosen oversized for a premises as lots of outside air is being brought in (replacing the condenser off exhaust air).
05-06-2009, 09:41 PM #15
05-06-2009, 09:57 PM #16
06-06-2009, 07:13 AM #17
Anyway, we speak here not about a window AC but a portable, and I can see from the anti-ad. that its comp is "clothed and buttoned".
By improper use it is possible to ruin everithing.
Can Anyone Help Me Find details of Precision Air Conditioners ?
By sam707 in forum Air ConditioningReplies: 7Last Post: 28-11-2008, 04:53 PM -
Portable Air Con Condenser box ?
By busman12 in forum Air ConditioningReplies: 2Last Post: 31-07-2008, 11:54 PM -
Portable AC as heatpump
By stuartsjg in forum Heat PumpsReplies: 6Last Post: 03-10-2007, 10:31 AM -
Portable Refrigeration Air Conditioner Units
By possum in forum FundamentalsReplies: 2Last Post: 23-07-2007, 02:47 PM -
PLEASE ADVISE: Re Portable A/C
By mordechai in forum Air ConditioningReplies: 3Last Post: 25-04-2007, 07:13 PM