    Post How good is your split system running?



    Hey folks, let's start a discussion on your basic split system.

    You all make me jealous with measuring SH or SC on cold rooms and chillers and being able to fine tune them with refrigeration fundamentals, but let's take a look at a basic split unit for comfort cooling:

    It has a capillary after the condenser on the outdoor unit that feeds a partially expanded liquid to the indoor unit where it evaporates in the coil, and depending on pipe run, may or may not completely evaporate before returning to the outdoor unit. They chuck in an accumulator to mop up any liquid. They will come pre-charged for pipe runs up to 50m, but you may only have a 10m pipe-run.

    Some of the very basic units will give you 1 access point for gauges on the suction valve on the outdoor unit.

    A typical check for good running would be air-on/air-off temperatures on the evaporator with a delta-T of 12 to 14 degrees, and ensuring a suction pressure above freezing. (hopefully) In fact, some technical help desks tell you to ignore the pressures and work on temperatures only.
    We all know that on critically charged systems, when performance is lacking, (after checking good airflow) we first do a "pressure test" and weigh out the charge and see if anything has been lost.

    In general if the evaporator off-coil temperature is below 10 degrees in cooling I am happy, and if the heat rejection outside is in the 30 degree range (fixed speed compressor) I am happy. [Depending of course on ambient]

    So the question is, do I need to get more technical with my measurements? Would trying to measure a subcooling value off the outlet of the condenser tell me much? The superheat values can vary so much.

    Before answering, please remember I am talking about a BASIC BASIC split system. No EEV's, no inverter driven compressors, but I will allow you a condenser fan speed controller!



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: How good is your split system running?

    Please clarify in what measuring system are your temperatures. I presume SI (Celsius).

  3. #3
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: How good is your split system running?

    You presume correct!! Wouldn't life be easier if we all stuck to one unit of measure!!

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: How good is your split system running?

    Quote Originally Posted by acnerd View Post
    You presume correct!! Wouldn't life be easier if we all stuck to one unit of measure!!
    Yes, that is why SI system is introduced and recommended for use in whole world.

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: How good is your split system running?

    When are you wanting to take these measurements? On a maintenace visit or a breakdown?

    If it was just a maintenance visit them usually temperatures alone can tell you if the system is running ok. No need to start taking subcooling and superheat measurements unless the system is first being commissioned or there is a problem with the unit.


    The reason most people say work on temperatures rather than pressures are because each refrigerant has different pressures
    but the temps needed around the system are always roughly the same no matter what gas it is e.g R22 4bar 0°C but R410 0°C is 7bar

    If there was a breakdown for example and you weren't getting cooling at your indoor and both your coils
    were clean and airflow was correct then you would have to connect your gauges and begin to check your temps around the system.
    Your subcooling is important because by measuring it you can check if you have enough or not enough liquid at your metering device once you are sure that you have the correct amount of liquid at you metering device then you start to look at your superheat.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: How good is your split system running?

    Thanks Marc, it would seem that I am doing enough. In reply to your question, it would be on maintenance and breakdown visits. I think temperatures can tell you a lot about system performance.

    I've read some of your posts and know your are well qualified, so here's a harder question. 2 identical splits : One has a "liquid line" of 10m, and the other 50m. Assuming they have no drop or lift (ie indoor and outdoor unit at same level), and all other influencing factors are identical, would they have the same subcooling value? The reason I ask is because the metering device is on the outdoor unit, so one line has a 10m run of flashing off liquid, and the other 50m?

  7. #7
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: How good is your split system running?

    Quote Originally Posted by acnerd View Post
    Thanks Marc, it would seem that I am doing enough. In reply to your question, it would be on maintenance and breakdown visits. I think temperatures can tell you a lot about system performance.

    I've read some of your posts and know your are well qualified, so here's a harder question. 2 identical splits : One has a "liquid line" of 10m, and the other 50m. Assuming they have no drop or lift (ie indoor and outdoor unit at same level), and all other influencing factors are identical, would they have the same subcooling value? The reason I ask is because the metering device is on the outdoor unit, so one line has a 10m run of flashing off liquid, and the other 50m?
    Subcooling is the amount of refrigerant up to the metering device and superheat is the amount of refrigerant after the metering device. (after the evaporator for multisync)

    They both should be in the same region of subcooling.
    (4-7K).
    You say one line is 10m and one is 30m but since this is 'after' the metering device this is no longer measured as 'subcooling' but instead 'superheat'. By measuring the superheat you can start to add refrigerant slowly to bring superheat up to around 7-10k??

    If the metering device was on the indoor ( very common with VRF's) then the liquid line would be long as you say and you would need to add refrigerant to increase the subcooling to 4-7K.
    Last edited by marc5180; 03-08-2009 at 09:42 PM.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  8. #8
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: How good is your split system running?

    OK. It's what I thought, but always trying to learn something new! Thanks again.

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: How good is your split system running?

    No probs...
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: How good is your split system running?

    Quote Originally Posted by marc5180 View Post
    Subcooling is the amount of refrigerant up to the metering device and superheat is the amount of refrigerant after the metering device.

    They both should be in the same region of subcooling.
    (4-7K).
    You say one line is 10m and one is 30m but since this is 'after' the metering device this is no longer measured as 'subcooling' but instead 'superheat'. By measuring the superheat you can start to add refrigerant slowly to bring superheat up to around 7-10k??

    If the metering device was on the indoor ( very common with VRF's) then the liquid line would be long as you say and you would need to add refrigerant to increase the subcooling to 4-7K.

    Run that by me again.

    Subcooling is a volume and superheat is a mixture of liquid and gas?

  11. #11
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: How good is your split system running?

    Quote Originally Posted by multisync View Post

    Subcooling is a volume and superheat is a mixture of liquid and gas?
    I've just re-read my post and im sure i didn't say that.

    Ok your being pedantic. Superheat is measured after the evaporator.
    Last edited by marc5180; 03-08-2009 at 09:44 PM.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  12. #12
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: How good is your split system running?

    Quote Originally Posted by marc5180 View Post
    I've just re-read my post and im sure i didn't say that.

    Ok your being pedantic. Superheat is measured after the evaporator.
    Originally Posted by marc5180
    Subcooling is the amount of refrigerant up to the metering device

    Plus it's not being 'pedantic' to point out you are completely wrong.
    Last edited by multisync; 03-08-2009 at 10:08 PM.

  13. #13
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: How good is your split system running?

    That's ok Multisync, I knew what Marc meant. As all 3 of us know, subcooling tells us if the charge is correct in the system; and that's why he said AMOUNT!!

  14. #14
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: How good is your split system running?

    Seeing as you know everything, rather than pick at my posts, why dont you help out answering questions on the forum?
    Or is that beneath you.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  15. #15
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: How good is your split system running?

    Nah, he's a one trick pony.

    Joking of course

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: How good is your split system running?

    Quote Originally Posted by acnerd View Post
    That's ok Multisync, I knew what Marc meant. As all 3 of us know, subcooling tells us if the charge is correct in the system; and that's why he said AMOUNT!!
    Subcooling doesn't tell you if the charge is right in capillary system like you speaking here.
    Superheat is what tells you if your charge is right.
    How much it should be, depend on design.
    Here are some text about that and some generic superheat tables.

  17. #17
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: How good is your split system running?

    Thanks Nike, I did know about that, but wasn't thinking of it. That's a good little document. Ta!!

  18. #18
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: How good is your split system running?

    Quote Originally Posted by marc5180 View Post
    Seeing as you know everything, rather than pick at my posts, why dont you help out answering questions on the forum?
    Or is that beneath you.

    I did, I told you you were wrong and wrong.

    Basically you didn't like it and pretended you didn't write what you obviously did and rather than saying "opps my bad" you thought the best way of deflecting attention was to attack me in a very unfriendly way.

  19. #19
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: How good is your split system running?

    If it was anyone else who had said it, then i would have said "oops my bad"
    Last edited by marc5180; 05-08-2009 at 08:03 PM.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Restricted split system license Australia
    By mak74 in forum Training
    Replies: 8
    Last Post: 05-04-2011, 06:26 AM
  3. Split type wall mounting Air Conditioning system
    By stevews in forum Air Conditioning
    Replies: 23
    Last Post: 11-07-2005, 09:55 AM
  4. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •