03-06-2009, 10:28 PM #1
York chiller with J body compressors
Hi all, could someone PLEASE give me the torque settings for the electical terminal posts on the J body recip compressors. I have already broken two from over tightening!
York in the the UK has been taken over by Johnson Controls and getting technical info a no way. I have the manuals for the chiller, but there aren`t any torque settings for any bolts. I am also replacing all the head and oil pump gaskets, so those settings would be a bonus.
Many thanks!
-
03-06-2009, 11:34 PM #2
Re: York chiller with J body compressors
Hi Burrah Boy
These are in LB.FT
Terminal Block 34-40
Terminal Stud (Nut) 20-25
Oil Pump 27-32
Access Cover / Top Head 78-90
Good Luck
-
04-06-2009, 07:04 AM #3
Re: York chiller with J body compressors
Burrah Boy
You may have been misled?
Because the early J comp studs are steel (copper coated).
The later ones are Copper and it is not easy to tell.
York recommend using a magnet to determine which type you have.
Because of this there are 2 torque settings dependant upon which stud you have.
The above torque is for steel and the copper is 19-22ft lbs
Grizzly
-
04-06-2009, 09:15 AM #4
Re: York chiller with J body compressors
Thanks Grizzly one! The ones I broke are the copper ones, and the new ones they sent seem to be steel!
-
04-06-2009, 09:16 AM #5
Re: York chiller with J body compressors
Sorry, forgot to thank TESLA to!
-
04-06-2009, 05:08 PM #6
Re: York chiller with J body compressors
Burrah Boy.
If you open the attached you will notice there is a gap between the top 2 nuts and the bottom one clamping the terminal post in place.
It is quite common for the fitter to bottom out the 2 top nuts against the bottom one.
Which will cause either the stud to shear or the baseplate to crack.
Therefore it is very important to hold the middle nut in place away from the base nut, whilst tightening.
This is a very common mistake!
You may well be aware of this but someone may benefit from the extra knowledge?
Grizzly
-
07-06-2009, 10:06 AM #7
-
07-06-2009, 03:42 PM #8
-
09-06-2009, 06:05 AM #9
Re: York chiller with J body compressors
Griz, you are a legend. Stand up and take a bow.
magoo
-
09-06-2009, 08:22 PM #10
Re: York chiller with J body compressors
I'll second or third that, i'd definately be lost without him!
al
Similar Threads
-
York Chiller problems
By ingherrera in forum CommercialReplies: 18Last Post: 26-07-2011, 03:10 PM -
Compressors - screw or reciprocating?
By Josip in forum Industrial CompressorsReplies: 18Last Post: 27-01-2009, 10:36 PM -
York Chiller startup when on Emergency Power
By Apollo10 in forum Trouble ShootingReplies: 3Last Post: 22-12-2008, 07:13 PM -
need help on YORK chiller
By nassersh in forum CommercialReplies: 4Last Post: 16-12-2008, 12:47 PM -
york chiller motor rotation error
By cesarnino in forum Trouble ShootingReplies: 7Last Post: 13-12-2008, 03:43 PM