    Shell and Tube Condenser in level with a Receiver



    Hello All,
    I kindly ask you to help me on following matter
    We have R404A installation with a rack of 5 piston compressors, with oil separators, oil level regulator...One shell and tube condenser with water regulating valve and a receiver. This installation also has 5 cooling rooms which work indipendently of the compressor rack.
    Is it possible to install shell and tube condenser at the same level as a receiver. Receiver is horisontal type with connection on the top of the receiver. This means that pipeline from condenser goes up to the receiver connection. Shell and tube condenser has around 15% reserve in capacity. Will this arragment cause operation problems?
    Thanks a lot.



  2. #2
    Join Date
    Jul 2008
    Location
    Houston Tx
    Posts
    42
    Rep Power
    0

    Re: Shell and Tube Condenser in level with a Receiver

    your going to back log liquid but it can be done..there are many way to do it but I would use a small pumper drum set up.

  3. #3
    Join Date
    Apr 2009
    Location
    South Africa
    Age
    49
    Posts
    108
    Rep Power
    16

    Re: Shell and Tube Condenser in level with a Receiver

    Its not wise to it it like that because u are going to loose to much condensing area in your cell due to liquid filling up the condenser.
    Rather take out the receiver and install a cell and tube condenser that are dual purpose as a reciever and condenser.