    Lg 36s accessive condensation



    hi boys
    i am working on two identical 36 s wall mount lg units.
    they both have less than 5 meter distance between outdoor and indoor unit.
    they both condensate too much that water is droping from the louver.
    the evaporator is wet therefore fan is throughing the water from front of the unit.
    suction and discharge are both frosting up ie gradually
    they both are r 410a.
    both units are two years old.
    any idea



  2. #2
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Lg 36s accessive condensation

    i think that the units if they are still putting weird charges in them are charged to 7.5 meters so you may find that they are over charged, filters ok?

  3. #3
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Lg 36s accessive condensation

    possibly lack of indoor air flow, short of gas, drainage problems? what is suction presuure/temp? are the units sized correctly or are they running all day long?

  4. #4
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: Lg 36s accessive condensation

    hi no problem on sizing the unit, no problem with drainage, charging i am not sure , last time i checked at the ambient of 25 c was 140 psig suction.
    the water is dripping from outlet air where fan ie placed.
    filters are ok
    i feel uncomfortable with the charge, maybe undercharged not sure

Similar Threads

  1. Condensation in duct
    By harsen in forum Fundamentals
    Replies: 6
    Last Post: 10-05-2009, 12:04 PM
  2. Condensation at supply air diffuser
    By Cofreth in forum Trouble Shooting
    Replies: 6
    Last Post: 19-02-2009, 07:50 PM
  3. Major Condensation Issues
    By Core-Mark TO in forum Trouble Shooting
    Replies: 1
    Last Post: 10-09-2008, 07:20 PM
  4. help - lots of condensation on insulated pipes
    By goldpau in forum Air Conditioning
    Replies: 16
    Last Post: 04-09-2008, 07:48 PM
  5. Linde condensation unit data
    By nike123 in forum Commercial
    Replies: 16
    Last Post: 08-06-2008, 12:49 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •