Good day gentlemen...
I have 2unit 15HP Semi Hermetic Compressors and in order to increase cooling capacity I have to add one more 10HP Compressor... another thing is, I have to replace the existing condensers due to old age.
Now the question is... is it possible to use 3 compressors working together on a single "appropriate" condenser? Why?....
Thanks for your time....
03-06-2009, 08:57 AM #2
Re: Parallel compressors single condenser
yes i think u can use single condensor, which should be designed to take the load of the three compressors, but when one of the compressors is put off, there is a un necessary energy waste,
03-06-2009, 12:21 PM #3
03-06-2009, 12:43 PM #4
You can use three compressors in parallel , it should preferably have an equal volumetric displacement . Besides, a very effective oil return system is key to success , probably use oil reservoir & oil level regulator for each compressor . Moreover, head pressure regulation will be essential in the event that one or two compressors are cylced off . I can help in designing high side system for the application. PM ddk0123@gmail.com
04-06-2009, 01:46 AM #5
dont forget balance line for sumps,one oil reservoir,one oil level control per compressor,check valves in discharge lines,correct suction header for oil return,maybe someone has a drawing out there somewhere,basically your making a rack.
04-06-2009, 04:26 AM #6
go to your wholsalers engineer give him conditions of operation it would be more probable financially to run single comp than build up a hashed rack,2 old donks,one new donk,rehash add extras try and make it look trade quality.im sure bitzer would have a packaged job to suit.new pipework,new evap,less warranty problems more reliability.
04-06-2009, 04:41 AM #7
You need to find someone that knows what there doing. The information you need is beyond the scope of this website. If it's not done properly you will have nothing but issues
04-06-2009, 04:47 AM #8
07-06-2009, 08:56 AM #9
Adding compressor does not necesarrily mean, you can acheive additional cooling capacity. You must check the design of entire system to acheive desired result result.
21-06-2009, 11:59 AM #10
Adding another compressor to the existing system, will need a re- assesment of the complete system, including piping design. That means suction header, discharge header, liquid line, suction line, condenser, receiver, oil management and controlling. You can add a different size compressor to the rack, as long as the smaller compressor is the lag compressor.
21-06-2009, 02:34 PM #11
Adding a third compressor to existing unit is impossible!
The condenser is designed to reject heat from the existing compressors.
If you want to add more compressors, you will need to design a new condenser, new pipes, new TXV....
Actually, you will be building a new unit.
21-06-2009, 03:05 PM #12
21-06-2009, 03:06 PM #13
21-06-2009, 03:08 PM #14
22-06-2009, 05:13 AM #15
gday peter where i was coming from about balance line was maintaining the same sump pressure in all comps essentally where their is a large difference between compressor capacities,thats how we used to make em.
22-06-2009, 09:01 AM #16
You only need a balance line if all the sumps are linked together, if you work with floats then you don't need them.
25-08-2009, 05:44 AM #17
Should there be a problem if you're building a new system with parallel compressors, and have chosen a condenser from the beginning to handle the load?
Seems that if this was designed from the start, you could eliminate problems before they could exist.
Shingoshi
how to put compressors in parallel
By Lc_shi in forum Technical SpeculationsReplies: 33Last Post: 19-12-2009, 07:30 AM -
Compressors - screw or reciprocating?
By Josip in forum Industrial CompressorsReplies: 18Last Post: 27-01-2009, 10:36 PM -
changing condenser and compressors
By seraaco in forum Supermarket RefrigerationReplies: 4Last Post: 17-01-2009, 11:55 PM -
parallel flow condenser design for appliance a.c
By saurabh_23jan in forum Air ConditioningReplies: 2Last Post: 14-11-2008, 06:12 AM -
suction and discharge head for parallel compounding compressors
By herman in forum CommercialReplies: 1Last Post: 11-10-2006, 08:32 PM