    Question excessive suction temp



    hi
    Iam new
    pls help me I am mechanical eng. but I am new in refrigeration system I have trouble with vilter single screw comp. work with 717R (ammonia) the suction temp in normal condtion is -30c & the pressure is 0.0 kpa. but now the suction temp is -7 c & the pressure still 0.0 kpa. there is no efficiency !!,where is the broplem?? how can I fix it?



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: excessive suction temp

    Quote Originally Posted by engiraq
    with 717R (ammonia) the suction temp in normal condtion is -30c & the pressure is 0.0 kpa. but now the suction temp is -7 c & the pressure still 0.0 kpa.


    This seems like a problem of not having enough liquid in the evaporator causing higher than normal suction superheat. I am assuming the compressor is fully loaded at 100% capacity.

    Last edited by US Iceman; 03-06-2009 at 02:18 AM. Reason: fixed quote
    If all else fails, ask for help.


  3. #3
    engiraq's Avatar
    engiraq Guest

    Re: excessive suction temp

    thanks iceman ,the capacity is 100%

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: excessive suction temp

    If the compressor is at 100% and you high suction superheat my logic (based on a very small amount of information) is this: there is just enough liquid entering the evaporator to keep the suction pressure high when the compressor is fully loaded. However, if the superheat starts to increase this tells me the evaporator is not fully wet with enough liquid to keep the superheat at the normal point.

    Therefore, the evaporator is evaporating what liquid is present and the resulting vapor is being superheated in the evaporator (which does very little actual cooling).

    How much liquid do you have in the high pressure receiver?
    If all else fails, ask for help.


  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: excessive suction temp

    Hi
    if system is at 100% and suction is rising, your client is overloading and system cannot cope, check motor amps, air on air off evap temperatures. Discharge pressures.
    Clients have a great habit of doing that and blame the system performance.
    Remember "heat in equals heat out ".
    magoo

  6. #6
    engiraq's Avatar
    engiraq Guest

    Re: excessive suction temp

    if you mean high pressure reciever that one contact with liquid pump it have much liquid a bove the 75% & liquid pump pressure is 4 bar its normal !!

  7. #7
    mattfromthecc's Avatar
    mattfromthecc Guest

    Re: excessive suction temp

    Have to agree with ICEMAN, not enough liquid in the evap, if everything else in Normal.

  8. #8
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: excessive suction temp

    What would happen if the TXV were to cut back the refrigerant flow too much?

    Wouldn't the evap over evaporate & hence push up the exit superheat?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  9. #9
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: excessive suction temp

    not enough NH³ in system ore blocking along the way back.

    Ice

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: excessive suction temp

    Quote Originally Posted by desA View Post
    What would happen if the TXV were to cut back the refrigerant flow too much?

    Wouldn't the evap over evaporate & hence push up the exit superheat?
    TXV on a NH3?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: excessive suction temp

    good one peter (lol)

    Ice

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. HIGH SUCTION LINE SURFACE TEMP WITH R22 @ 60psig
    By TRASH101 in forum Refrigerants
    Replies: 7
    Last Post: 15-03-2007, 07:52 PM
  4. Excessive Superheat
    By AEGIS Cool in forum Technical Discussions
    Replies: 13
    Last Post: 26-11-2006, 08:06 PM
  5. Suction temp
    By Temprite in forum Commercial
    Replies: 18
    Last Post: 30-05-2005, 10:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •