    Vilter oil loss



    I have 2 systems both with Vilter compressors. One is a 450xl, single compressor, the other uses two 350 es compressors. Both systems have been in service for 20 years. Even with rebuilt or brand new compressors installed I am getting oil past the seperator(s) and not returned to the crankcase(s) I think oil is leaving more when they are unloaded and maybe in so fine a mist that it's going right thru the seperator. I am wanting to adjust Hot gas bypass to allow more time fully loaded. Both systems have had numerous problems and lots of people working on them over the years. Too many cooks? no doubt. Any body have thoughts on tuning this to minimize oil losses?



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Vilter oil loss

    Quote Originally Posted by squidward
    I am wanting to adjust Hot gas bypass to allow more time fully loaded.
    I would not do that. You will increase the amount of energy use by 25%-33% depending on how many additional cylinders load up.

    The usual causes for oil carryover are:

    Higher than normal suction superheat
    liquid slugging
    frequent starting & stopping
    etc, etc.

    Is any oil returning from the the separators back to the compressor crankcase?
    If all else fails, ask for help.


  3. #3
    Join Date
    Nov 2008
    Location
    USA
    Posts
    34
    Rep Power
    0

    Re: Vilter oil loss

    OK. The system with the 450xl got a brand new compressor during the last outage. It runs 98% of the time, all year long. The suction pressure fluctuates between 61 and 68 psi or so(target of 65) I have not yet heard the hot gas bypass come on at all- on a startup the suction pressure went as low as 54 psi, still no HG bypass. We capture the history on the plant computer. Also they've been running with the evap. float level control screwed all the way in and calling for liquid out of the receiver all the time. Which of course there is none, "we just add ***** til it comes up to the level in the evaporator" I also found a broken capillary tube to the TCvalve in the coolant line of the oil cooler- Hot oil! I'll be back over ther tommorrow to adjust that float, add R-22 and see if I can get that hot gas working.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Vilter oil loss

    Quote Originally Posted by squidward
    Also they've been running with the evap. float level control screwed all the way in and calling for liquid out of the receiver all the time.
    Sounds like you have a lot of other problems besides oil loss. My guess is: something else besides the compressor is causing the oil loss.
    If all else fails, ask for help.


  5. #5
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Vilter oil loss

    Hi Squidward;
    It sounds like you have a lot of problems. I have worked on a lot of systems with multiple problems over the years and sometimes you cannot get the money to fix them all.
    Iceman is correct that you have a lot of other problems besides oil loss.
    My drill on oil loss from Recips is to see if oil is coming back at all. If it is not I clean the float and lines etc.
    I assume your discharge temps are not too high.
    You may have blown the oil separators. Do they have a replaceable element?

  6. #6
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: Vilter oil loss

    squidward,

    It seems that low pressure receiver is starving and it calls for a liquid all the time keeping the solenoid valve busy.adjust that float and see if it liquid rise from the vessel.check regulator superheat setting, starving regulator results to low comp oil level even if you have an efficient oil separator.
    abet

  7. #7
    Join Date
    Nov 2008
    Location
    USA
    Posts
    34
    Rep Power
    0

    Re: Vilter oil loss

    Thanks, Yeah I know it has multiple problems. I am working to fix the obvious ones, and both units continue to improve..I put in a new needle and seat in the oil return float, do not have replaceable elements, don't think I have a superheat regulator. Suction temp is 41 deg.F and 65 psi/38 deg makes my superheat 3 deg. F. I'll have to check it on a hot day as well. Mostly running unloaded right now.

  8. #8
    Join Date
    Nov 2008
    Location
    USA
    Posts
    34
    Rep Power
    0

    Re: Vilter oil loss

    Well allright! It seems that you can't blame any one thing for this oil loss condition. All you can do is fix those items that you know need fixing, and when all that is fixed, system running stable, oil loss goes away!

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Vilter oil loss

    All you can do is fix those items that you know need fixing, and when all that is fixed, system running stable, oil loss goes away!
    Just like magic!

    You will often find many small problems contribute in ways you might not expect.

    My first law of refrigeration is: The problem is seldom the major piece of equipment. The major equipment is reacting to how the system operates.

    People often fall into the trap of saying the equipment is at fault and most often it is not. You will usually find something else caused the equipment to break.
    If all else fails, ask for help.


  10. #10
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Vilter oil loss

    Quote Originally Posted by US Iceman View Post
    Just like magic!


    My first law of refrigeration is: The problem is seldom the major piece of equipment. The major equipment is reacting to how the system operates.
    I think this is usually the problem; thats why I believe there is no replacement of a good knowledgeable operator! A operator that knows his system inside and out is worth a whole lot in my book.

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Vilter oil loss

    I would agree with you nh3wizard. I keep seeing people who think the equipment is not operating properly and want to adjust it.

    Here is a scenario: system is perceived to not be cooling adequately. Result? Adjust an expansion valve or add more refrigerant.

    Answer? More training and education is required. That is not a slap at anyone. This is a complicated industry!

    The more interesting problems are where someone tries to force the system to operate the way they think it should. I'll bet you have seen this also.
    If all else fails, ask for help.


Similar Threads

  1. Oil Loss 250 VLD Mycom Screw
    By Keith1977 in forum NH3
    Replies: 23
    Last Post: 20-09-2008, 12:28 PM
  2. looking for a book *Friction loss for pIpe*
    By ydoubleun in forum Fundamentals
    Replies: 11
    Last Post: 11-07-2008, 06:26 AM
  3. Noise induced hearing loss damages
    By Abe in forum Legal-Business-Marketing
    Replies: 7
    Last Post: 26-05-2008, 10:36 AM
  4. Vilter Cool Compression Mono Screw
    By Steve Mackie in forum NH3
    Replies: 13
    Last Post: 08-05-2008, 11:18 PM
  5. Vilter 440VMC Block heater info needed
    By Sun Dragon in forum Industrial Compressors
    Replies: 0
    Last Post: 14-01-2007, 06:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •